04-09-2012, 07:08 PM #1
Service equipment or not?
So, I just inspected a rural property. The electrical panel that I would have designated "service equipment" was located adjacent to the driveway. Meter and main disconnect. Neutral/ground are bonded together.
The next panel in the series is in the garage. This also had a disconnect and the neutral/grounds are bonded together. I believe this is incorrect, but wanted to make sure. If I understand it, you can only have one service equipment.
This was a very special property It had an "ace maker", a "suer pump", a "landry" and a "bedroon". Don't find many of those, that's for sure.
Amazing.
Similar Threads:Department of Redundancy Department
Supreme Emperor of Hyperbole
http://www.FullCircleInspect.com/
-
04-09-2012, 07:24 PM #2
Re: Service equipment or not?
The way I understand your description, the garage panel is wrong by having the bond strap installed and the neutrals and grouding conductors mixed on the buss.
All answers based on unamended National Electrical codes.
-
04-09-2012, 07:31 PM #3
Re: Service equipment or not?
-
04-09-2012, 09:14 PM #4
Re: Service equipment or not?
Jim & Jerry,
Thanks. There is a 4-wire feed from the service equipment and a ufer. But, that would be acceptable, right. It's the neutral/ground that is the problem.
Department of Redundancy Department
Supreme Emperor of Hyperbole
http://www.FullCircleInspect.com/
-
04-10-2012, 05:14 AM #5
Re: Service equipment or not?
The 4 wire feeder would be correct. The grounds not isolated from the neutrals and the case bonding are the problems.
All answers based on unamended National Electrical codes.
-