Results 1 to 4 of 4
  1. #1
    Ryan Stouffer's Avatar
    Ryan Stouffer Guest

    Default Distribution Panel

    Does this ground have to be isolated on a separate lug or does this look acceptable? This is at the distribution panel.

    Thanks,

    Ryan

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Crawl Space Creeper

  2. #2
    Join Date
    Aug 2008
    Location
    Maryland
    Posts
    1,970

    Default Re: Distribution Panel

    Are you asking about the AL conductor?


  3. #3
    Ryan Stouffer's Avatar
    Ryan Stouffer Guest

    Default Re: Distribution Panel

    No the aluminum ground. it is in the middle of the copper grounds. behind the neutral.


  4. #4
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,040

    Default Re: Distribution Panel

    Quote Originally Posted by Jim Port View Post
    Are you asking about the AL conductor?
    Quote Originally Posted by Ryan Stouffer View Post
    No the aluminum ground. it is in the middle of the copper grounds. behind the neutral.
    I think you are both referring to the same conductor???

    If so, that would be okay as I am sure that terminal bar is rated for either copper and aluminum (I did not say rated for "both" as that might indicate to some that "both" could be in the same terminal).

    If all the white painted conductors are grounds and not white neutrals, they would all be allowed in that terminal bar.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •