    Why would sparky put Aluminum antioxidant paste on Copper ?

    Would you call this out? He has this in all the panels on a commercial building.

    Best

    Ron

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Member Benefits1

  2. #2
    Join Date
    Mar 2007
    Location
    Columbus GA
    Posts
    3,747

    Default Re: Aluminum antioxidant paste on Copper ?

    I do not see the paste on the aluminum connector though.
    Strange.???

    ' correct a wise man and you gain a friend... correct a fool and he'll bloody your nose'.

  3. #3
    Join Date
    Aug 2008
    Location
    Maryland
    Posts
    1,970

    Default Re: Aluminum antioxidant paste on Copper ?

    You may not see the paste because it is not required.


  4. #4
    Join Date
    Mar 2007
    Location
    Columbus GA
    Posts
    3,747

    Default Re: Aluminum antioxidant paste on Copper ?

    I said "Strange" because the paste IS on the copper but NOT on the aluminum.

    Last edited by Rick Cantrell; 07-18-2010 at 07:25 AM.
    ' correct a wise man and you gain a friend... correct a fool and he'll bloody your nose'.

  5. #5
    Join Date
    Apr 2008
    Location
    Western Massachusetts
    Posts
    536

    Default Re: Aluminum antioxidant paste on Copper ?

    Quote Originally Posted by Ron Bibler View Post
    Why would sparky put Aluminum antioxidant paste on Copper ?

    Would you call this out? He has this in all the panels on a commercial building.
    How do you know it's "aluminum" antioxidant paste and not a copper or multi-purpose antioxidant paste?

    The purpose of antioxidant paste on aluminum is because aluminum oxide is an insulator. The antioxidant is applied to aluminum conductors to ensure optimal electrical conductance and reduce overheating.

    Some electricians also apply it to copper, particularly with aluminum lugs.


  6. #6
    Philip's Avatar
    Philip Guest

    Default Re: Aluminum antioxidant paste on Copper ?

    So it is the aluminum lugs which mandates the paste. Would not need it al to al. Looks like the Sparky knew what he was doing.


  7. #7
    Join Date
    Apr 2008
    Location
    Western Massachusetts
    Posts
    536

    Default Re: Aluminum antioxidant paste on Copper ?

    Quote Originally Posted by Philip View Post
    So it is the aluminum lugs which mandates the paste. Would not need it al to al. Looks like the Sparky knew what he was doing.
    While some local jurisdictions may require its use, the NEC does not require anti-oxidant compound, except so far as it defers to the manufacturer's instructions. It does mention its use however. Whether the Al lugs require the compound or not would therefore depend on the manufacturer and locality.

    All the same, it is probably a good idea to use the anti-oxidant compound when working with aluminum to minimize oxidation and the potential thermal problems that accompany it.


  8. #8
    John Steinke's Avatar
    John Steinke Guest

    Default Re: Aluminum antioxidant paste on Copper ?

    Keep in mind that lugs often come with some manner of compound already in them. The amounts of the compound vary, as does the final appearance of the connection.


  9. #9
    Join Date
    Apr 2009
    Location
    Manchester, Vermont
    Posts
    298

    Cool Re: Aluminum antioxidant paste on Copper ?

    Has anyone on this site, ever done inspection where they might have
    seen a copper wire corroded at its terminal connections? Any yes some
    lug come pre - load with a corrosion resistance compond.


  10. #10
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,040

    Default Re: Aluminum antioxidant paste on Copper ?

    Quote Originally Posted by Robert Mattison View Post
    Has anyone on this site, ever done inspection where they might have seen a copper wire corroded at its terminal connections?

    Yes.

    In corrosive environments, such as along the beach (thinking Atlantic Ocean and Intra Coastal Waterway here, both saltwater - and, where I inspect, we are between the two, and the two are less than 1/2 mile apart, we are on a barrier island).

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  11. #11
    Mitchell Toelle's Avatar
    Mitchell Toelle Guest

    Default Re: Aluminum antioxidant paste on Copper ?

    Quote Originally Posted by Robert Mattison View Post
    Has anyone on this site, ever done inspection where they might have
    seen a copper wire corroded at its terminal connections? Any yes some
    lug come pre - load with a corrosion resistance compond.
    Bakersfield...120+ miles inland...no obvious reason for finding this, but we do occasionally.

    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images

  12. #12
    Christel Hunter's Avatar
    Christel Hunter Guest

    Default Re: Aluminum antioxidant paste on Copper ?

    I've done a little research on oxide inhibitor, here's an excerpt from an article I authored that was published in IAEI News in 2006:

    Oxide inhibitor use is considered good workmanship for all 600-volt terminations, whether wired with copper or aluminum conductors. The oxide inhibitor provides a barrier at the connection point that excludes moisture and other potentially damaging environmental substances. Oxide inhibitor must be compatible with the conductor type. Different manufacturers make compounds that can be used with copper only, aluminum only, or both copper and aluminum. Be sure to choose the compound listed for the application. Compression connectors often come pre-filled with the appropriate oxide inhibitor. When connectors are tested for compliance with UL 486B, the conductor is prohibited to be wire brushed or abraded, and oxide inhibitor may only be used if the connector is pre-filled with the antioxidant. Therefore, mechanical set-screw terminations are tested without wire brushing and oxide inhibitor.
    According to the UL GuideInfo (UL White Book) for wire connectors (ZMVV), oxide inhibitor for aluminum or copper wire may be used if the connector manufacturer recommends its use on the connector documentation. Oxide inhibitor is of the most value when making connections between uncoated copper and aluminum. This type of connection is subject to galvanic corrosion when in the presence of an electrolyte. Since most lugs today are made of tin-plated aluminum, galvanic corrosion is limited except in the case of severe electrolytic environment or significant damage to the connector plating.


  13. #13
    Bert de Haan's Avatar
    Bert de Haan Guest

    Default Re: Aluminum antioxidant paste on Copper ?

    Quote Originally Posted by Jerry Peck View Post
    Yes.

    In corrosive environments, such as along the beach (thinking Atlantic Ocean and Intra Coastal Waterway here, both saltwater - and, where I inspect, we are between the two, and the two are less than 1/2 mile apart, we are on a barrier island).
    And in sub panels. (You let the opportunity slide so I took it. )


  14. #14
    Denny Waters's Avatar
    Denny Waters Guest

    Default Re: Aluminum antioxidant paste on Copper ?

    I believe I read in Doug Hansen's book "Electical Inspection of Existing Dwellings" that it helps with torquing down the lugs as well.


  15. #15
    Bill Nolte's Avatar
    Bill Nolte Guest

    Default Re: Aluminum antioxidant paste on Copper ?

    Quote Originally Posted by Robert Mattison View Post
    Has anyone on this site, ever done inspection where they might have seen a copper wire corroded at its terminal connections? And yes some lugs come pre-loaded with a corrosion resistance compound.
    You will always see corrosion on copper terminations in residential or commercial swimming pool equipment rooms, Waste Water Treatment Plants and Water Treatment Plants. Correct oxide inhibitor is always a good idea whether required or not. I have seen copper corrode where exposed at the terminations in less than a week in Waste Water Treatment Plants on new installs. It's a shame the engineers didn't know to require oxide inhibitor in their project specifications.
    Always remember NFPA70 the National Electrical Code is the minimum for safety and not necessarily the best design criteria.


  16. #16
    Join Date
    Jul 2008
    Location
    Snowbird (this means I'm retired and migrate between locations), FL/MI
    Posts
    4,086

    Default Re: Aluminum antioxidant paste on Copper ?

    Quote Originally Posted by Bill Nolte View Post
    You will always see corrosion on copper terminations in residential or commercial swimming pool equipment rooms, Waste Water Treatment Plants and Water Treatment Plants. Correct oxide inhibitor is always a good idea whether required or not. I have seen copper corrode where exposed at the terminations in less than a week in Waste Water Treatment Plants on new installs. It's a shame the engineers didn't know to require oxide inhibitor in their project specifications.
    Always remember NFPA70 the National Electrical Code is the minimum for safety and not necessarily the best design criteria.
    I disagree. You will see when the installation and area is violative of the code in either its use, maintenance, or design.

    It is an indication that the system has not been designed or maintained (and the area not designed and/or maintained) correctly.

    Equipment must be designed and maintained (and area) so as to protect equipment from the effects of corrosion and chemicals. Storing disinfecting chemicals in the area and/or not properly designing the area and zone for the correct CATEGORY of hazardous conditions.

    The code is not a design/engineering manual.


  17. #17
    Bill Nolte's Avatar
    Bill Nolte Guest

    Default Re: Aluminum antioxidant paste on Copper ?

    Quote Originally Posted by H.G. Watson, Sr. View Post
    I disagree. You will see when the installation and area is violative of the code in either its use, maintenance, or design.

    It is an indication that the system has not been designed or maintained (and the area not designed and/or maintained) correctly.

    Equipment must be designed and maintained (and area) so as to protect equipment from the effects of corrosion and chemicals. Storing disinfecting chemicals in the area and/or not properly designing the area and zone for the correct CATEGORY of hazardous conditions.

    The code is not a design/engineering manual.
    The simplistic view related above shows a potential lack of real world experience and forethought. NFPA 70 “The National Electrical Code” is a design manual! It is the minimum for safety design allowable by law, as stated previously. The code also states that compliant designs may not be the best or most efficient design. If the NEC were not a design manual it could not be quoted for corrections to non-compliant installations.
    Waste water treatment plants have many corrosive elements, some atmospheric, that are impossible to keep out of the equipment; the equipment can only be designed to mitigate the intrusion of these corrosive elements into the enclosure. Similarly the electrical terminations within a pool equipment room are exposed to chlorine vapors by the very nature of the location of the pumps. Although the load center or panel board and related controls do not have to be located adjacent to the motors, a disconnect should be so located for safety reasons and by such location the disconnect is also exposed to corrosive vapors. NEMA 4X stainless steel or fiberglass enclosures help to mitigate the corrosive effects but they do not eliminate such effects.
    Per your statements design and maintenance would also eliminate the need for hazardous locations sections of the code. Nothing could be further from the truth. Hazardous location requirements are also designed to mitigate (the effects of an explosion), not to prevent one.
    I stand by my statement that anti-oxidant compounds are a good idea. All metals corrode over time, some just faster than others and frequently due to atmospheric contaminants. The anti-oxidant is a cheap, simple, safe way to extend the life of terminations, especially those exposed to damp or corrosive atmospheres!


  18. #18
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,040

    Default Re: Aluminum antioxidant paste on Copper ?

    Quote Originally Posted by Bill Nolte View Post
    You will always see corrosion on copper terminations in residential or commercial swimming pool equipment rooms, Waste Water Treatment Plants and Water Treatment Plants.
    Quote Originally Posted by H.G. Watson, Sr. View Post
    I disagree. You will see when the installation and area is violative of the code in either its use, maintenance, or design.

    It is an indication that the system has not been designed or maintained (and the area not designed and/or maintained) correctly.

    Equipment must be designed and maintained (and area) so as to protect equipment from the effects of corrosion and chemicals. Storing disinfecting chemicals in the area and/or not properly designing the area and zone for the correct CATEGORY of hazardous conditions.

    The code is not a design/engineering manual.
    Quote Originally Posted by Bill Nolte View Post
    The simplistic view related above shows a potential lack of real world experience and forethought. NFPA 70 “The National Electrical Code” is a design manual!
    Let's start here: (underlining and bold are mine)
    - From the 2008 NEC.
    - - ARTICLE 90 Introduction
    - - - 90.1 Purpose.
    - - - - (C) Intention. This Code is not intended as a design specification or an instruction manual for untrained persons.

    I.e., the code IS NOT a design manual. The simply stated MINIMUM REQUIREMENTS which are to be incorporated into the design of electrical systems.

    Now let's go to the other comment regarding location for the electrical equipment:
    - 110.11 Deteriorating Agents.
    - - Unless identified for use in the operating environment, no conductors or equipment shall be located in damp or wet locations; where exposed to gases, fumes, vapors, liquids, or other agents that have a deteriorating effect on the conductors or equipment; or where exposed to excessive temperatures.
    - - - FPN No. 1: See 300.6 for protection against corrosion.
    - - - FPN No. 2: Some cleaning and lubricating compounds can cause severe deterioration of many plastic materials used for insulating and structural applications in equipment.