    Southwest US
    Default Unusual main breakers
    I don't remember running into this before. It is an older ITE panel, now a branch panel but I beleive was originally the service panel. It has 2 40 amp 2-pole breakers side by side, each breaker feeds the bus below it. It seems that each 2-pole breaker feeds 1 leg of the bus. I guess this would be an 80 amp main breaker?
    Should they have a common handle tie?
    END GLOBAL WHINING
    Default Re: Unusual main breakers
    Yes, those two breakers should be tied together with a tie-bar. Good luck finding one, but then he improvised that far and should have finished it.
    I think I see the grounding bus joined to the neutral lug with a black jumper that runs under the new main breakers. That is wrong for a submarine panel.
    Screw grounding that bus to the panel box - right, no screw grounding the neutral bus - right. Neutral jumper - right, Jumper from neutral lug to the grounding bus - wrong.
    Southwest US
    Thanks John.
    The jumper was cut, here's a closer crop.
    I am not sure the grounding bus was bonded to the panel however, if it was I didn't see it.
    Nevermind, I see the bonding screw you are referring to.
    END GLOBAL WHINING
    Dennis Webber's Avatar
    Dennis Webber Guest
    An electrician needs to be brought in, IMO.
    Garry Blankenship's Avatar
    Garry Blankenship Guest
    If it's a sub-panel, the grounding & bonding look OK. No need for the main, but since it's there, it is supposed to be secured mechanically to the panel. Definitely must have a handle tie, but agree you're not gonna find it, unless a complete factory unit. I do not like it and think it's funky, but this idea of using two C/Bs as additive overload protection on the same phase, evidently is, ( or at least was ), legal.