    Are the main lugs ever rated for more than one conductor? This is an ITE Pushmatic box with 200 Amp disconnect. Is there any definitive code or standard covering this issue? Under what circumstances, if any, is this allowed? I have seen this a number of times and I haven't been able to find any standards regarding it. If it is just manufacturers documentation, how do we find this?

    THanks for the help.


    Member Benefits1

  2. #2
    Join Date
    Dec 2007
    Location
    Osceola, AR
    Posts
    311

    Default Re: Double Tapped Main Lugs

    It's wrong.
    1. Lugs are for one conductor unless it is stamped on the lug.
    2. When a lug is rated, listed and labeled for more than one conductor they usually are required to be the same size.
    3. There is probably no overcurrent protection for the circuit tapped off the lug except the utility company fuse at the pole or transformer.

    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Alton Darty
    ATN Services, LLC
    www.arinspections.com

  3. #3
    Join Date
    Mar 2007
    Location
    Spring Hill (Nashville), TN
    Posts
    5,851

    Default Re: Double Tapped Main Lugs

    As Alton noted, it is wrong and I find it fairly often in old panels. Being a Pushmatic, I doubt you will easily find a reference from the manufacturer. I would not worry about documenting that it is wrong, call it out and just say it is wrong and needs an electrician to correct.

    Sometimes we are too concerned about providing proof to justify our findings when simply reporting what we find is all that is needed. If someone wants proof let them find the proof that it is correct!

    Scott Patterson, ACI
    Spring Hill, TN
    www.traceinspections.com

  4. #4
    Join Date
    Aug 2012
    Location
    Columbus, Ohio
    Posts
    89

    Default Re: Double Tapped Main Lugs

    Quote Originally Posted by Scott Patterson View Post
    As Alton noted, it is wrong and I find it fairly often in old panels. Being a Pushmatic, I doubt you will easily find a reference from the manufacturer. I would not worry about documenting that it is wrong, call it out and just say it is wrong and needs an electrician to correct.

    Sometimes we are too concerned about providing proof to justify our findings when simply reporting what we find is all that is needed. If someone wants proof let them find the proof that it is correct!
    Thanks.


  5. #5
    Join Date
    Oct 2009
    Location
    michigan
    Posts
    421

    Default Re: Double Tapped Main Lugs

    Quote Originally Posted by Scott Patterson View Post
    As Alton noted, it is wrong and I find it fairly often in old panels. Being a Pushmatic, I doubt you will easily find a reference from the manufacturer. I would not worry about documenting that it is wrong, call it out and just say it is wrong and needs an electrician to correct.

    Sometimes we are too concerned about providing proof to justify our findings when simply reporting what we find is all that is needed. If someone wants proof let them find the proof that it is correct!
    Incorrect! Everything IS leagal untill proven otherwize. Otherwize, only opinions would be necessary instead of legal standards. It is this type of mind set that leads to abuse.

    Missing from the pics that have been posted of legal (approved) multi-conductor terminals: There are terminals rated/approved for two conductors under one set screw. I've used them many times, usually in commercial and industrial equipment. Manufacturers often have these as options.
    These terminals are characterized by oval or what appears like two holes connected togeather.
    They are quite obvious upon observation.


  6. #6
    Join Date
    Aug 2012
    Location
    Columbus, Ohio
    Posts
    89

    Default Re: Double Tapped Main Lugs

    Quote Originally Posted by bob smit View Post
    Incorrect! Everything IS leagal untill proven otherwize. Otherwize, only opinions would be necessary instead of legal standards. It is this type of mind set that leads to abuse.

    Missing from the pics that have been posted of legal (approved) multi-conductor terminals: There are terminals rated/approved for two conductors under one set screw. I've used them many times, usually in commercial and industrial equipment. Manufacturers often have these as options.
    These terminals are characterized by oval or what appears like two holes connected togeather.
    They are quite obvious upon observation.
    Thanks for the additional info. The ones in question in this panel did not have an oval shape.


  7. #7
    Join Date
    Aug 2008
    Location
    Maryland
    Posts
    1,970

    Default Re: Double Tapped Main Lugs

    To Bob S, I disagree. Driving 60 in 40 is always illegal, it just becomes a problem when caught. Installing work not in conformance with the standards enforced is illegal, whether it mleads to a problem or not.

    Since those are not multi-conductor terminals they are not code compliant. If the NEC has been adopted that would then be a violation of a legally adopted standard.


  8. #8
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,040

    Default Re: Double Tapped Main Lugs

    Quote Originally Posted by bob smit View Post
    Incorrect! Everything IS leagal untill proven otherwize.
    That's like saying that when a tree falls in the forest because there is no one around to hear the sound.

    It is illegal (I dislike that term in this instance) WHETHER OR NOT someone is caught or something is proven or not.

    A tree falling in the forest DOES make the very same noise ... whether or not anyone is there to hear it.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  9. #9
    Join Date
    Dec 2007
    Location
    Chico,Ca
    Posts
    454

    Default Re: Double Tapped Main Lugs

    Even if you could apply tap rules & IMO they do not apply in this case, it fails miserably.


  10. #10
    Join Date
    Dec 2008
    Location
    Maryland
    Posts
    2,809

    Default Re: Double Tapped Main Lugs

    Quote Originally Posted by Jerry Peck View Post
    It is illegal (I dislike that term in this instance) WHETHER OR NOT someone is caught or something is proven or not.

    .

    Maybe we should use "not just or true" for "illegal" ?


    Rollie;
    Please elaborate on "it fails miserably."


  11. #11
    Join Date
    Aug 2008
    Location
    Maryland
    Posts
    1,970

    Default Re: Double Tapped Main Lugs

    I believe Rollie is talking about how it does not come close to meeting the tap rules properly.

    - - - Updated - - -

    I believe Rollie is talking about how it does not come close to meeting the tap rules properly.

    - - - Updated - - -

    I believe Rollie is talking about how it does not come close to meeting the tap rules properly.

    All answers based on unamended National Electrical codes.

  12. #12
    Join Date
    Aug 2011
    Location
    Bennett (Denver metro), Colorado
    Posts
    1,461

    Default Re: Double Tapped Main Lugs

    Quote Originally Posted by bob smit View Post
    Incorrect! Everything IS leagal untill proven otherwize. Otherwize, only opinions would be necessary instead of legal standards. It is this type of mind set that leads to abuse.
    I don't think that came out the way you intended.
    Quote Originally Posted by bob smit View Post
    There are terminals rated/approved for two conductors under one set screw. I've used them many times, usually in commercial and industrial equipment. Manufacturers often have these as options.
    These terminals are characterized by oval or what appears like two holes connected togeather.
    They are quite obvious upon observation.
    You can put two ground wires of the same gauge under the same lug in a service panel, but I'm unaware of any allowed terminal that you can put wires of different gauges under the same lug.

    If you choose not to decide, you still have made a choice.

  13. #13
    Join Date
    Feb 2009
    Location
    Southern Vancouver Island
    Posts
    4,607

    Default Re: Double Tapped Main Lugs

    Hey bob.
    A 200 amp disconnect feeds that large conductor.

    Someone has slipped a #10 or similar gauge wire in there. It's a no-brainer.

    John Kogel, RHI, BC HI Lic #47455
    www.allsafehome.ca

  14. #14
    Join Date
    Oct 2009
    Location
    michigan
    Posts
    421

    Default Re: Double Tapped Main Lugs

    Quote Originally Posted by Lon Henderson View Post
    I don't think that came out the way you intended.

    You can put two ground wires of the same gauge under the same lug in a service panel, but I'm unaware of any allowed terminal that you can put wires of different gauges under the same lug.
    Thanks for being the only one who didn't jump to inference Lon.


  15. #15
    Join Date
    Mar 2007
    Location
    Cape Cod, Massachusetts
    Posts
    614

    Default Re: Double Tapped Main Lugs

    Are these neutral lugs the approved type or is this illegal also?

    - - - Updated - - -

    Are these neutral lugs the approved type or is this illegal also?

    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Ken Amelin
    Cape Cod's Best Inspection Services
    www.midcapehomeinspection.com

  16. #16
    Join Date
    Aug 2008
    Location
    Maryland
    Posts
    1,970

    Default Re: Double Tapped Main Lugs

    Ken, they still look like the standard lug that Square D uses that is only for one cnductor.

    All answers based on unamended National Electrical codes.

  17. #17
    Join Date
    May 2009
    Location
    Washington State
    Posts
    376

    Default Re: Double Tapped Main Lugs

    Quote Originally Posted by Jerry Peck View Post
    That's like saying that when a tree falls in the forest because there is no one around to hear the sound.

    It is illegal (I dislike that term in this instance) WHETHER OR NOT someone is caught or something is proven or not.

    A tree falling in the forest DOES make the very same noise ... whether or not anyone is there to hear it.
    Just like if a Man is in the woods, and there is no Woman around for a 100 miles, He's "STILL" Wrong !


Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •