Results 1 to 4 of 4
  1. #1
    Jeff Eastman's Avatar
    Jeff Eastman Guest

    Default Not tightly bounded

    ..........

    Last edited by Jeff Eastman; 12-11-2007 at 07:45 PM.
    Member Benefits1

  2. #2
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,040

    Default Re: Not tightly bounded

    Is the second photo showing 4 different twists and connections for that neutral/grounded conductor?

    If so, that's a super no-no.

    The other one, eh, maybe, if by itself, but, if the above is correct, have the electrician check it out while on-site making repairs to the above.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  3. #3
    dan orourke's Avatar
    dan orourke Guest

    Default Re: Not tightly bounded

    Quote Originally Posted by Jerry Peck View Post
    Is the second photo showing 4 different twists and connections for that neutral/grounded conductor?

    If so, that's a super no-no.
    Okay, super Jerry you got me. I'm like totally not understanding!!

    What do you mean 4 differnent twists and & connections, what exactly are you refering to?


  4. #4
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,040

    Default Re: Not tightly bounded

    Looks like that neutral/grounded conductor was too large for any one terminal when it was twisted together, so they twisted it together in 4 separate 'cables' so it would fit into those terminals.