    One, should grounds be isolated from neutral bus on first panel (closest to service feed) and is there any problem with aluminum service neutral from Utility? Three 100 amp panels for each unit.

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Member Benefits1

  2. #2
    Join Date
    Mar 2007
    Location
    Santa Rosa, CA
    Posts
    3,154

    Default Re: 2 Q's on 3 flat

    Looks like service equipment. Neutral and grounds are required to be bonded together in the service equipment and separated at any downstream panels.

    Department of Redundancy Department
    Supreme Emperor of Hyperbole
    http://www.FullCircleInspect.com/

  3. #3
    Join Date
    Jul 2007
    Location
    Chicago
    Posts
    187

    Default Re: 2 Q's on 3 flat

    Thanks GA.


  4. #4
    Join Date
    Mar 2007
    Location
    Ft. Myers, FL
    Posts
    363

    Default Re: 2 Q's on 3 flat

    Both are fine.

    Paul Kondzich
    Ft. Myers, FL.

  5. #5
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,040

    Default Re: 2 Q's on 3 flat

    Quote Originally Posted by Ross Neag View Post
    One, should grounds be isolated from neutral bus on first panel (closest to service feed)

    Gunnar said "Looks like service equipment."

    That is true ... *IF* ... that is the service equipment.

    Let's clarify that it is ... the main disconnect in those panels are the first main disconnects, right?

    No other disconnects ahead of them.

    No 'main disconnect' for the service with these fed from that, right?

    I ask because you said:
    Three 100 amp panels for each unit
    Which indicates to me that there should be (likely is?) a single service to the building which then supplies these, which would make these "non-service equipment" panel with main disconnects. Nothing wrong with that, I actually prefer them that way, that allows the occupant to have 'one main' to turn everything off with.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  6. #6
    Join Date
    Mar 2007
    Location
    Santa Rosa, CA
    Posts
    3,154

    Default Re: 2 Q's on 3 flat

    JP,

    He did say "service feed". I assume that if he meant "main disconnect" he would have said it. However, it wouldn't be the first time I've been wrong (today).

    Department of Redundancy Department
    Supreme Emperor of Hyperbole
    http://www.FullCircleInspect.com/

  7. #7
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,040

    Default Re: 2 Q's on 3 flat

    Quote Originally Posted by Gunnar Alquist View Post
    JP,

    He did say "service feed".

    Actually, this is what he said:
    on first panel (closest to service feed)
    "closest to service feed"

    To me ... that means there is the service ... and somewhere near there are those panels ... but (as I was asking) where are 'the first main service disconnects'?

    In those panels or before those panels?