Old 05-15-2007, 07:48 PM
A/C disconnect box wiring
Last edited by Jeff Eastman : 12-19-2007 at 04:29 PM. Reason: correct subject line
Home inspection
Old 05-15-2007, 09:15 PM
Thom Walker's Avatar
Re: Jeff Eastman
Jeff,
Do you have other pictures of the panel?
- Paul Fix
Old 05-15-2007, 09:34 PM
Re: Jeff Eastman
It's wrong (unless that wire nut is rated for both copper and aluminum).
But not any more wrong than that low voltage in there (which I'm sure you wrote up).
Old 05-16-2007, 07:19 AM
Rick Cantrell Rick Cantrell is offline
Re: Jeff Eastman
Low voltage wires/cables are not permitted to be in the same box, conduit or raceway as house wiring.
First of all it's a safety issue, next the low voltage lines can, will and do pick up induction interference from the higher voltage ac lines, causing a lot of problems with low voltage equipment.
Rick Cantrell
Old 05-16-2007, 12:35 PM
Jim Luttrall Jim Luttrall is online now
Re: Jeff Eastman
Jeff, the low voltage cables could become energized by the high voltage cables, kind of like water and electricity, they are best kept separated.
Aluminum and copper connections are not allowed since the two dissimilar metals react and corrode which causes poor connections and overheating. The two metals must be connected through an approved method which keeps them apart. A twisted connection with a wire nut of any kind is not acceptable.
Mr. Inspector.net, Inc.
Allen, Texas 75002
  #6 (permalink)
Old 05-16-2007, 12:46 PM
Bruce Breedlove's Avatar
Bruce Breedlove Bruce Breedlove is offline
Re: Jeff Eastman
Aluminum has a higher coefficient of expansion than copper. When an aluminum wire is heated (e.g., by current flowing through the wire) it will expand more than the same sized copper wire. When aluminum and copper wires are connected together this difference in expansion can cause the connection to become loose. A loose connection can cause arcing. Arcing can cause a fire.
Common wire nuts are not designed to accomodate the different expansion rates of aluminum and copper. Special wire nuts and connectors are available for aluminum-copper connections and are usually purple in color.
Bruce Breedlove
www.avaloninspection.com
Home inspection
vB.Sponsors
Ad Management by RedTyger
