Old 06-02-2007, 11:11 AM
John Stephenson John Stephenson is offline
Outlets under soffits
Home inspection
Old 06-02-2007, 12:24 PM
David Banks David Banks is offline
Re: Outlets under soffits
2003 IRC
E3802.3 Outdoor receptacles
All 125 volt single phase,15-and 20 ampere receptacles installed outdoors shall have ground- fault circuit interrupter protection for personnel.
Exception Section E4001.7
E4001.7
Snow melting and deicing equipment.
Outdoor receptacles that are not readily accessible and are supplied from a dedicated branch circuit for electric snow melting or deicing equipment shall be permitted to be installed without ground- fault circuit interrupter protection for personnel.However, ground fault protection for equipment shall be provided for fixed outdoor electric deicing and snow melting equipment.
I put this in my reports for exterior covers. Do not have NEC for covers.
: Recommend exterior receptacles have protective weather covers that are weatherproof whether or not plug cap is inserted.
Dave
Old 06-02-2007, 12:35 PM
Not the one in the photo, at least no in my opinion.
David posted code for GFCI protection, not weather proof covers, and, of course, it should have GFCI protection.
Old 06-02-2007, 04:08 PM
Scott Patterson's Avatar
I think it is OK as well.
Scott Patterson
Similar Threads
Exterior light fixtures and recept. outlets Jeff Eastman Electrical Systems: Home Inspection and Commercial Inspection 1 05-08-2007 05:39 PM
Testing GFCI Outlets Roger Kautz Electrical Systems: Home Inspection and Commercial Inspection 10 04-30-2007 07:30 AM
CPSC Recall: Floor Electrical Outlets Brian Hannigan Electrical Systems: Home Inspection and Commercial Inspection 0 04-18-2007 12:29 PM
vB.Sponsors
Ad Management by RedTyger