Main Panel
These are pictures of main service panel. Both of the grounds from SEC are attached to neutral bar and the A/C wiring is grounded at neutral bar also. I know that grounds and neutrals can be connected at main panel but shouldn't there be a grounding bar?
F.I.R.E. provides fireplace education, consulting services, fire investigation and litigation support across the United States.
Old 03-19-2010, 02:53 PM
fritzkelly fritzkelly is online now
Re: Main Panel
Tom, all 3 of these bars are already bonded by the configuration of the panel. You can't see the neutral SEC in your picture, it is connected to the bar on the far left in the enclosure above. The green grounds or white stripe neutrals you are looking at are going out to other equipment or panels.
"Only the government would believe that you could cut a foot off the top of a blanket, sew it to the bottom, and have a longer blanket" Wise Indian remarking on daylight saving time
Old 03-19-2010, 03:13 PM
Re: Main Panel
Thanks fritz, It has a been a long week and I just could not get my mind wrapped around this.
Old 03-19-2010, 06:26 PM
Jerry Peck's Avatar
Re: Main Panel
Quote:
Tom,
Here is some different wording you should try using and, when you are through reading this, you should see why.
Those are picture of "service equipment". Both of the grounds from "the feeders" are attached to the neutral bar and the A/C wiring is grounded at the neutral bar also. I know that grounds and neutrals "must be" bonded together at the "service equipment".
By recognizing that as "service equipment" you should be able to immediately recognize that the "service entrance conductors" are hidden behind the interior dividers within the combination meter/service equipment and you do not see them - all you see are the bus bars coming down from the hidden area above: the neutral/ground on the left and which is one and the same; the two hot phase legs in the center.
Looks like you have two mains going to remote panels and the other main breaker must be for the a/c condenser unit. All the conductors coming from those mains are "feeder conductors".
FREA Home Inspector Insurance
Share |
Similar Threads
Main Panel under the tub chris mcintyre Electrical Systems: Home Inspection and Commercial Inspection 8 03-02-2010 05:17 PM
Main Panel Jody Humbert Electrical Systems: Home Inspection and Commercial Inspection 9 06-17-2009 09:23 PM
Main Disconnect(s) vs Main Service Panel Michael Chambers Electrical Systems: Home Inspection and Commercial Inspection 8 06-11-2009 06:15 AM
Feed From Main Panel to Sub Panel Nick Ostrowski Electrical Systems: Home Inspection and Commercial Inspection 7 05-25-2008 05:38 PM
main panel Jerome W. Young Electrical Systems: Home Inspection and Commercial Inspection 7 01-04-2008 01:37 PM
Copyright ©2000 - 2010, Jelsoft Enterprises Ltd.
vB.Sponsors
Ad Management by RedTyger