Old 07-13-2007, 05:49 PM
David Banks David Banks is offline
Re: Ceiling fan & clearances from tub
Lights and fans shall not have any parts located within a zone measured 3 feet horizontally and 8 feet vertically from the top of the bathtub rim or shower stall threshold. This zone is all encompassing.
Dave
Old 07-13-2007, 05:50 PM
Richard Rushing's Avatar
I don't. But, if I were doing a code inspection, it would be from the outside edge to three (3) feet out and eight (8) feet up.
(see attached).
Richard Rushing, HCRI
Duncanville, Tx.
Old 07-13-2007, 06:40 PM
Envision a box over the tub (or shower) which is measured from Point A, measure out 3 feet, up 8 feet (or to the ceiling if less than 8 feet up), then back to the walls.
The tips of the blades of the ceiling fan are not allowed to cross into that 'box'.
Old 07-14-2007, 12:24 PM
Quote:
Originally Posted by RobertSmith View Post
Richard, by your comment you imply that if you pull out a measuring tape and measure things you are doing a code compliant inspection! Or am I misunderstanding you????
Robert-- that was a funny post. Yes... you were misunderstanding me.
Question: RE: Ceiling fan & clearances from tub --"Where do you measure from the tub to the edge of the paddles, on the inner rim (point a) or outer rim of tub (point b)?"
Answer: "I don't. if I were doing a code inspection, it would be from the outside edge to three (3) feet out and eight (8) feet up.(see attached)."
What part of the above answer means that taking any measurement (you said, "pull out a tape measure and measure things")... constitutes a code inspection? You have to put it in the context of the question that was asked and the answer I posted.
It is a rare occassion that I pull out a measuring tape during an existing property inspection. However, a new construction is another story-- I do use one, as a new construction inspection is basically a code inspection, whether anyone wants to acknowledge it or not. You are inspecting to what the builder is building to-- present day code.
The essence of what I was saying was that I rarely use a tape measure unless it's a new construction.
If I see something on an existing construction that looks like it could be a measureable code violation, I simply state what I see. Take a staircase for example, a home that has been lived in for 10-15 years will NEVER have the staircase torn-out and re-done because a measurement is off. If I see something that is visually obvious, I will report what I see and move on.... Pretty simple.
Rich
Duncanville, Tx.
Similar Threads
propane clearances John Arnold Heating, Ventilation, Air Conditioning (HVAC): Home Inspection and Commercial Inspection 11 09-04-2008 02:32 PM
Tub Installation Clearances Joseph P. Hagarty Plumbing System: Home Inspection and Commercial Inspection 9 06-30-2007 10:58 AM
Prefab Fireplace Clearances Bruce Breedlove Fireplaces, Chimneys and Solid Fuel Burning Appliances: Home Inspection and Commercial Inspection 3 05-26-2007 07:58 PM
Stucco clearances Michael Vasquez Building Envelope: Home Inspection and Commercial Inspection 8 05-11-2007 06:55 PM
Clearances for Panel Jeff Eastman Electrical Systems: Home Inspection and Commercial Inspection 3 05-02-2007 02:53 PM
vB.Sponsors
Ad Management by RedTyger