07-27-2007, 06:32 PM
plug adapters
07-28-2007, 06:00 AM
Re: plug adapters
For starters, does the AHJ allow that "dedicated" garage door outlet to be non-GFCI?
If not, and that is (should be) a GFCI, looks to me like that the adapter/transformer combinaiton prevents activating the GFCI's internal test circuitry.
07-28-2007, 08:33 AM
Re: plug adapters
Quite to the contrary.
That outlet in 'on the ceiling', i.e., it is not considered "readily accessible" and thus does not require GFCI protection anyway.
The strange thing about that photo is - I see a duplex receptacle and I see TWO things plugged into it ... what to heck is that triple tap for anyway? Remove it. Problem solved.
Now, *IF* that is the ONLY receptacle in the garage, you have a different problem - where is the garage receptacle?
07-28-2007, 10:11 AM
Re: plug adapters
I don't see a problem. Those adapters are listed, and it is quite possible to use them without creating a hazard.
I'm just curious what the transformer powers; I can't think of anything else you're likely to hang on the ceiling!
07-28-2007, 12:47 PM
Re: plug adapters
Per the model code, not, it's not. Per, for example the AJH in my community, that needs to be GFCI.... and a *individual* GFCI protected receptacle outlet is required at *each box *over a kitchen counter, and some other such things....)
07-28-2007, 12:53 PM
Re: plug adapters
A lot of times the adapters have a max watt rating.... the ones I've seen are around 600W. So, if they have a space heater plugged into it that would be wrong... Otherwise, as mentioned, they can be used safely.
07-28-2007, 05:17 PM
Re: plug adapters
Michael,
That's some strange wording there. Is that yours, or the code?
What that states is 'no duplex receptacle is allowed over the kitchen counter.
A GFCI breaker, or a GFCI receptacle protecting downstream receptacle outlets would fulfill that requirement for GFCI protection - as stated. Each receptacle outlet does not need to be a GFCI device.
07-28-2007, 05:28 PM
Re: plug adapters
There doesn't appear to be a need for the adapter. As Jerry indicated, removing it solves the problem. I am more concerned with the breach of the fire barrier in the ceiling.
07-28-2007, 07:05 PM
Re: plug adapters
Michael Thomas: “If not, and that is (should be) a GFCI, looks to me like that the adapter/transformer combination prevents activating the GFCI's internal test circuitry.”
Apart from whether or not there is a requirement for the outlet to be GFCI protected, (which there isn’t in MD for this application), don’t forget there are GFCI breakers too.
| Thread Tools |