Old 10-10-2007, 05:55 PM
Dave Hahn Dave Hahn is offline
Service Entrance questions and terminology
OK, I'm seeing this panel type with more frequency and am not sure I'm representing things properly or using the correct terminology.
Usually a meter box is naturally locked (w/utility lock) and on this panel type I typically can't see what I see here, but instead would only see what's accessible from the service equipment side.
So what I usually get to see are four #1 AWG copper conductors connected to a 200-Amp "quad-pole" (terminology?) main service disconnect. But with access to the meter box here, I now see that there's 4/0 AWG aluminum conductors attached to the meter AND THEN the four #1's from the meter to the disconnect (see photos).
Assumptions:
(i) #1 CU has a 150-amp capacity. 4/0 AL has a 200-amp capacity.
(ii) I'm required by SOP to report service amperage and service entry conductor type.
QUESTION(S):
Without being able to see what I see in this case, I'd say that the service "capacity" (not required to report) was 300-amps (?) because of the double #1 CU, but that the service amperage was 200-amp due to the disconnect, and the SEC type was CU.
But in fact, isn't the "capacity" 200-amp due to the 4/0 AL, the service amperage still is 200-amp due to the disconnect, and the SEC type is AL ??
If the SEC is the 4/0 AL, which I normally wouldn't see in a lateral, what do I call the four #1 CU ??
Dave
Old 10-10-2007, 06:08 PM
Re: Service Entrance questions and terminology
Quote:
That is a 'combination meter/service equipment' enclosure, with both in the same enclosure.
Quote:
Assumptions:
Not quite right there. You are applying the ratings given in the notes to the ampacity tables, which do not apply to the service lateral side of the service (the conductors coming up from the bottom at the meter side in your photo). Those ratings only apply to the service entrance conductors in (for dwelling units only, not even commercial, for non-dwelling unit ratings you would need to refer to 310.15 Ampacity Tables.
QUESTION(S):
No, the service ampacity (amperage) and "capacity" are one and the same. That being the lowest of all the ratings, in this case, the 200 amp main disconnect.
You've lost me there, I'm not understanding what you are asking.
Those are not the service entrance conductors (SEC), those are the service laterals.
[quote] what do I call the four #1 CU ??[/quote
Those are the service entrance conductors (SEC).
I hope that helped.
Old 10-11-2007, 10:44 AM
brian schmitt brian schmitt is offline
dave,
the 4/0 al conductors for underground service usually are provided and installed by the poco. it is on their side of the meter. do not concern yourself with these as they are secured by the poco to prevent power theft. the 4 #1 copper wires and the main disco are a factory installed assembly and not your concern either. check stuff after the 200 amp disco if you want to do something!
Old 10-11-2007, 07:10 PM
Quote:
Which is why I did not say anything about the too sharp bends ... if the electrical contractor made those bends, the bends would be too sharp, but being as those bends are part of a UL listed assembly, those sharp bends are okay.
Nonetheless, though, the service laterals coming up into the box should be sealed around at the conduit, which looks like it should have a bushing.
Also, see that rusty looking shot pin in the back of the meter side of the enclosure? That was shot through the flat back of the enclosure and should have been shot through the standoff feet, seen to the right of it. The standoff feet are there to provide the REQUIRED 1/4" air space between the back of the enclosure and the wall, and when shot through the back like that one was, the back if now *pulled tight* to the wall - no 1/4" air space.
Similar Threads
Main Service Entrance Panel Tom Payne Electrical Systems: Home Inspection and Commercial Inspection 4 09-17-2007 06:29 PM
Terminology help Clay E White Roofing System: Home Inspection and Commercial Inspection 6 08-11-2007 09:27 PM
Service conduit bonding at service equipment Michael Thomas Electrical Systems: Home Inspection and Commercial Inspection 0 08-07-2007 06:59 AM
garage door terminology wes owens Exterior Systems: Home Inspection and Commercial Inspection 4 06-09-2007 01:29 AM
Service point terminology Michael Thomas Electrical Systems: Home Inspection and Commercial Inspection 12 06-05-2007 11:07 AM
vB.Sponsors
Ad Management by RedTyger