Page 1 of 2 12 LastLast
Results 1 to 65 of 73
    Feb 2011
    Port Orange, FL
    Default any electrical code prevent GFI outlet wired to GFI breaker
    Aug 2008
    Default Re: any electrical code prevent GFI outlet wired to GFI breaker
    No rule against this, but it is unnecessary as the breaker is already supplying the gfi protection.
    - - - Updated - - -
    Aug 2011
    Yes, there is a rule against it although I dunno why, but redundant GFCIs on the same circuit is not allowed.
    Would you mind pointing that rule out?
    There is no rule prohibiting it, not that I know of, other than common sense and nuisance tripping of a GFCI which is not where you would be looking to reset it. But code does not cover common sense anyway.
    I agree with Jerry, noting wrong with other than what he noted and I'll add it is a waste of money.
    Aug 2008
    Not according to the NEC. Please quote your source.
    Aug 2011
    I sit corrected. Some years ago I saw an episode of Holmes on homes where he said you could not do this. Later an electrician confirmed that you couldn't have redundant GFCI's. And I just never looked into it any further.
    It's a condition that I do not report on.
    Sep 2014
    Tennessee
    Holmes is in Canada. I liked watching the show, but they made some stupid recommendations on electrical installations.
    The other day I was watching Holmes on Homes and Mike was grabbing at a bunch of K&T wiring in a basement, and said, "all this knob and tube has to go its aluminum"!
    Aug 2011
    In the years since, I've learned a lot more about our man Holmes. I still like the guy, but he isn't the last word.
    I'm going to start teaching Home Inspection at a local school here and this has reminded me that I should do some research into some of the things that I've been thinking and saying for years that I learned from "old timers".
    Atlanta, Georgia
    Get yourself a copy of Code Check Complete. Everytime you think one of these truisms, review code check. It helps.
    - - - Updated - - -
    Aug 2011
    I've got copies of Code Check, Code, Electrical books, and books on soil analysis, plumbing, construction and more out my arse. I don't have the time to go through everything I've been told. That one about GFCIs wasn't crazy enough to warrant investigation.
    Jan 2011
    Marietta, Georgia
    I always report redundant GFCIs. If you don't, you will probably get that phone call sometime down the road asking why a GFCI tripped but it won't reset. Best to explain it to your client at the time of the inspection then later when you have forgotten. Besides, redundant protection is almost always a sign that someone with insufficient experience has been doing some wiring in the home. Makes me look just a little bit closer at the rest of the home's wiring.
    Quote Originally Posted by Michael Bronner View Post
    Define "report".
    I disagree.
    I have found many in new construction, having been done by electricians.
    I would agree if you had stated that it is an indication of someone who did not know, did not care, or was not paying attention ... to what they were doing (all three or which can apply to new construction at various times).
    From what i recall, GFCI panel breakers trip at a much higher amperage than GFI receptacle breakers, which to me, makes the GFI receptacle much safer. 50 milliamps vs 6 milliamps I think. I shocked myself with a gfi once, so i can imagine that 8 times the milliamps would hurt much more.
    Oct 2009
    michigan
    Quote Originally Posted by chris brown View Post
    Correct me if wrong, but I suspect you are confusing GFI with GFP ?
    Robin Wells's Avatar
    Robin Wells Guest
    Quote Originally Posted by Mike Twitty View Post
    He sometimes does work in US.. but vast majority in Toronto. But there is no code preventing it in Canada.
    Robin Wells Guest
    Think you may be thinking of AFCI when quoting 50 ma. Breaker GFCI trip p at 5 to 6 ma.
    Quote Originally Posted by bob smit View Post
    I suspect the same thing.
    The 50 ma ground-fault protection was for the equipment. The 5 ma ground-fault circuit interrupter protection is for personnel.
    Completely different breakers and different uses.
    Aug 2008
    There are two classes of gfi protection, Class A 5 MA and Class B 30 MA.
    Robin Wells Guest
    Well 10 ma can kill you.
    here is good article.. http://www.nema.org/Products/Documen...esentation.pdf
    Quote Originally Posted by Robin Wells View Post
    Well 10 ma will kill you.
    Not if the GFCI trips at 5 ma +/- 1 ma first ... ...
    (Whether GFCI breaker or GFCI receptacle.)
    Reporting is one thing, calling it a fault is something else again.
    I notice when I test the receptacle GFCI with a tester, often as not the GFCI breaker in the panel will trip first. So I don't think you can say one is better than the other.
    Marshall Brown's Avatar
    Marshall Brown Guest
    From a practical standpoint one of the darn thing will always trip before the other and Murphy will guarantee the one that trips is not the one you tested. One of the corollaries to this is that the one that did trip is concealed somewhere and serves the game filled freezer. DAMHIKT!
    - - - Updated - - -
    Using the test button on the GFCI outlet will NOT trip any other GFCI on that circuit.
    Using the built in test button is THE approved method for testing a GFCI.
    Using a plugin tester on a GFCI outlet is pointless.
    A plug in tester will tell you whether the outlet is grounded or not.
    True
    I should have said, (and was thinking), using the test button of a plugin tester on a GFCI outlet is pointless.
  29. #29
    Robin Wells Guest
    Isn't a class b set to trip at 20 ma.
    I disagree.
    Using the GFCI test button on a GFCI tester in a remote receptacle outlet will tell you if that remote receptacle outlet is GFCI protected. (As will testing the remote receptacle, going back to the GFCI receptacle, pressing the test button, going back to the remote receptacle to see if it is now off, then going back yet again to the GFCI receptacle to press the reset button - seems to me that the GFCI tester test button is pretty useful.)
    Using the GFCI tester test button when plugged into the GFCI receptacle, well, that is not "pointless", more like "redundant" ... not needed, but it works, however, the GFCI receptacle (or GFCI breaker) test button IS the approved test method.
    I disagree.
    Surprise
    I am talking about GFCI outlets, only.
    I think you know that.
    You say "redundant" --"not or no longer needed or useful; superfluous."
    I say "pointless" --- "having little or no sense, use, or purpose."
    Lets see
    So if using the test button of a plugin tester is redundant (not needed, not useful, or superfluous). How is it not pointless (having no use or purpose)?
    If you use the plugin tester and it trips the GFCI do you, or do you not use the test button on the GFCI? Of course you use the built in test button of the GFCI outlet. That makes using the plugin in tester "pointless".
    If you use the test button of a plugin tester and it does not trip, do you report the GFCI as defective? No. You use the builtin test button. Thus making the use of the plugin,,, POINTLESS.
    Either way, the built in test button must be used to determine it the GFCI outlet is functioning or not. Therefore using a plugin tester to test the GFCI outlet is not redundant, it's pointless.
  32. #32
    Robin Wells Guest
    The plug in tester will or should work in all cases except where there is no ground present. The plug in tester will show quickly other problems such as reversal.. depending on tester you use perhaps other info as well. Having said that, some of the info is interesting but really beyond SOP. (and if not understood can be dangerous to know .. too much information! )
    Personally I like the plug in tester.. I can see if the receptacle not only trips when testing, but also that everything is wired properly. If you use only the test button, the ground could be absent, and if it is a newer home, I really do want to know that.
    While it will test and trip by the test button when the plug in tester fails, if the plug in tester works and trips properly then it really does go one step further. So while not necessarily 100% something you require, I do not feel it is pointless as it does give you additional information and takes no longer really.
    But maybe that is because my background is electrical..
  33. #33
    Again, I said; using the TEST BUTTON on the plugin tester is pointless on a GFCI outlet.
    I did not say anything about the no ground, or reversed wiring.
    For those, the plugin tester does give useful information.
  34. #34
    Surprise
    Lets see
    (bold is mine)
    redundant
    adjective re·dun·dant \ri-ˈdən-dənt\
    : repeating something else and therefore unnecessary
    —used to describe part of a machine, system, etc., that has the same function as another part and that exists so that the entire machine, system, etc., will not fail if the main part fails
    : dismissed from a job because you are no longer needed
    Full Definition of REDUNDANT
    1 a : exceeding what is necessary or normal : superfluous
    b : characterized by or containing an excess; specifically : using more words than necessary
    c : characterized by similarity or repetition <a group of particularly redundant brick buildings>
    d chiefly British : no longer needed for a job and hence laid off
    2 : profuse, lavish
    3 : serving as a duplicate for preventing failure of an entire system (as a spacecraft) upon failure of a single component
    The GFCI tester test button is a redundant test to the GFCI device test button - EITHER will work, one is preferred and normal (the built-in test button)
    pointless
    adjective point·less \ˈpȯint-ləs\
    : having no meaning, purpose, or effect
    Full Definition of POINTLESS
    1 : devoid of meaning : senseless <a pointless remark>
    2 : devoid of effectiveness : flat <pointless attempts to be funny>
    The GFCI tester's test button DOES serve a purpose and is therefore not "pointless", it is, in fact, "redundant".
    True
    Sorry, Rick. The test button on the plug-in tester gives us info the receptacle test button does not provide.
    It tells us if the GFCI will trip if a faulty appliance is plugged into it. The built-in button don't do dat.
    It tells us if a receptacle is protected by a GFCI somewhere else. The built-in button don't do dat.
    It tells us if the outlet is still energized after tripping. The built-in button don't do dat.
    You should always do both tests.
  36. #36
    Yes it does.That is exactly what the GFCI is for.
    Only if the downstream GFCI trips first, and is wired in series.
    I think GFCI's do indicate power. I know mine do.
    I'm not saying don't use the plugin tester. They have their uses. I'm saying, don't rely on the plugin test button to replace the builtin test button on a GFCI outlet.
    There are new inspectors reading this thread that may think it's acceptable to use the plugin test button instead of using the builtin test button on the GFCI outlet.
    All this talk just confuses the proper method.
    The proper and approved method to test a GFCI is with the built in test feature.
  37. #37
    Yes there are units that have a little light, but I find fairly often they are faulty or wired wrong, so the receptacle stays hot after tripping, while downstream receptacles are maybe protected.
    You said it was pointless, but you meant something else?
    The manufacturer says use the button but they don't encounter and maybe don't care about the bad wiring. Works fine but it is installed wrong.
    Just retract your confusing statement and it all comes clear.
  38. #38
    I did not say don't use a plugin tester at all for anything ever.
    I said, using the TEST button of a plugin tester on a GFCI outlet is pointless.
    For testing the GFCI feature of a GFCI outlet, using the test button of a plugin tester is pointless.
  39. #39
    Aug 2011
    Is a GFCI receptacle ever defective if it trips with the tester test button?
  40. #40
    Mar 2008
    Charlotte NC
    Trick question right! Answer: Only if it doesn't reset. (and the smoke doesn't get out).
  41. #41
    Redundant, yes.
    Pointless, no.
    You can try to skew it any way you want ... but using the GFCI tester test button is "redundant" ... a "back up" test ...that basically the definition of "reduredundant".
    Redundant, yes.
    Pointless, no.
    Having a discussion with you is pointless because you are so redundant.
    Just kidding, but I couldn't resist the pun.
  43. #43
    Mar 2013
    Washington, DC
    Redundant, yes.
    Pointless, no.
    Warning! Thread Drift
    What about the upcoming requirements for "Self Testing" GFCI protection? I understand why they will be required, but I don't understand the mechanics of how they self test.
    Would two self testing GFCI outlets affect each other somehow?
    - - - Updated - - -
    Redundant, yes.
    Pointless, no.
  44. #44
    Mar 2013
    Washington, DC
  45. #45
    Let me rephrase what I think your question is.
    Could a GFCI be defective even if it tripped when tested using a plugin tester?
    Not likely, but yes it could.
    Conversely
    Could a GFCI be functioning properly if it did not trip when tested with a plugin tested.
    Again, not likely, but yes.
    That is why I say not to use the test button of a plugin tester on a GFCI outlet.
    Who really knows what is going on inside a plugin tester, or even a GFCI?
    Was the plugin tester calibrated to the same standards.
    Is the plugin tester still within the allowed standards?
    We just do not know. We don't know if the GFCI is within the allowed standards either, but we do know that using the built in test button is always approved.
  46. #46
    Mar 2008
    Charlotte NC
    Conversely
    Pushing the built in test button does not find: 1) worn out contacts; 2) loose connections; 3) multiple GFCI devices. Doesn't seem pointless to me.
    If we only listen to the fox the hen house might not be so safe!
  47. #47
    Aug 2011
    I think extremely unlikely, and even more unlikely that any test that we can do would find whatever defect it has.
    Conversely
    Agree assuming that the tester indicates a grounded plug, but even if it then trips when pressing the GFCI test button, I still write it up as not reacting to the tester's button. If the tester's button doesn't trigger the GFCI, then will a real ground fault through a person trip it?
    Agree, but I don't agree that the tester is pointless when using it on a GFCI. It doesn't offer a definitive result, but then HIs don't do the type of testing that is definitive.
    In general, the three blade tester is one of our most useful tools. A HI with 200 inspections under his/her belt, has or should have, used it on over 6000 receptacles. You often see tiny variances in the glows that indicate something is wrong like weak grounds, crossover current bleeding, and poor blade retention. Since the tester isn't designed to show these defects, I don't write up a diagnosis based on a flickering light, but rather call for an electrician to evaluate and correct.
  48. #48
    Rick, stop pushing our buttons!
    PS, 3-light testers don't need calibration. They simply short to ground. That is why they won't trip the GFCI if the grounding is poor or missing.
    I had a standard outlet in a bathroom yesterday. Of course I needed to use my tester's test button, although I could have used a wire jumper or a paper clip.
  49. #49
    Good one John
    Not exactly. They have a resistor in them. If it was "They simple short to ground", what do you think would happen if you pressed the test button on an unprotected outlet.
    The term "calibration", may not be the best word to use, but they are in some way calibrated for resistance to ground. BTW resistors do go bad.
    If you use the paper clip I hope there is a working GFCI ahead of the outlet
  50. #50
    John,
    Are you testing for GFCI protection tripping off, or for breakers tripping?
    Robin Wells Guest
    Agreed. Although this would not point out a poorly wired or missing ground or false ground.
    Conversely
    Agreed again. Although this should lead you to being and wonder what is the reason, and very likely something worth making a note of. If it does not trip with a plug in tester but does trip with a test button.. worth noting I would suggest.
    Say what you want, but I like to test as closely to real life scenario as possible, and simply pressing a test button does not meet that in my books.
    - - - Updated - - -
    Agreed.. is a resister that lets 5 ma of current pass to ground. I did have one torn apart in shop. Think was a 20K (or somewhere thereabouts) 1/2 watt resistor.
  52. #52
    I calculated 22k for 5ma at 120v
  53. #53
    John,
    Just a bit of sarcasm. When nothing tripped, I went upstairs and tripped the GFCI then back down to test for power. Then wrote it up.
  54. #54
    Something many people don't know is that a GFI receptacle may not immediately reset. If you wait 1/2 hour it may then reset.
    I have had two cases where a homeowner/agent was upset that an outlet was disabled after the test. (threatened to charge me for the electrician who came to repair). Of course, we are required to test and it isn't our "fault".
    - - - Updated - - -
  55. #55
  56. #56
    Mar 2008
    Charlotte NC
    - - - Updated - - -
    If I have to wait more than 5 seconds, I'm writing it up as faulty!
  57. #57
    If the GFCI trips and isn't able to be immediately reset ...
    ... THERE MAY BE A PROBLEM WITH THE CIRCUIT ... or the GFCI. Quite possibly not the GFCI.
    Mar 2008
    Charlotte NC
    If it didn't fail until I tested it, I'm going 9:1 GFCI. Either way it "requires further investigation by licensed electrician" .
  59. #59
    Ummm ... haven't you read the thread about "self testing GFCIs"?
    I could very well be a ground-fault which was "trying to trip" the "stuck" (for lack of a better term) GFCI, but once tripped by the test button, the tripping action is now free to trip as it should ... didn't you read that thread about "self-testing" GFCIs?
    That is why I say it could either be the GFCI ... OR ... the circuit, and not wanting "the circuit" to be bad and presume that the GFCI is the problem - *I* would check both.
    It very well might be the GFCI is bad in and of itself, but ... what if both the GFCI AND the circuit were found to be bad (that is another possibility).
    Electrician does not need to "evaluate" the circuit OR the GFCI ... ... the electricians just need to "test" the circuit with his/her equipment, and replace the GFCI (the best and easiest way to "test" a GFCI device is to replace it - if the replacement does the same thing, sure, there *could* be two bad GFCIs, but at that point I'd do more testing on the circuit).
    Aug 2011
    Are you kidding me!
    An electrician is evaluating the circuit or the GFCI when he/she tests with his/her equipment.
    Your comment was like deja vu watching Bill Clinton parse "is".
    But it was funny...
  61. #61
    Mar 2008
    Charlotte NC
    I could very well be a ground-fault which was "trying to trip" the "stuck" (for lack of a better term) GFCI, but once tripped by the test button, the tripping action is now free to trip as it should ... didn't you read that thread about "self-testing" GFCIs? Didn't you notice? I was one of the malcontents!
    That is why I say it could either be the GFCI ... OR ... the circuit, and not wanting "the circuit" to be bad and presume that the GFCI is the problem - *I* would check both. I did not know you were a licenced electrician.
    It very well might be the GFCI is bad in and of itself, but ... what if both the GFCI AND the circuit were found to be bad (that is another possibility). ​I wonder what the definition of "evaluate" is?
    Electrician does not need to "evaluate" the circuit OR the GFCI ... ... the electricians just need to "test" the circuit with his/her equipment, and replace the GFCI (the best and easiest way to "test" a GFCI device is to replace it - if the replacement does the same thing, sure, there *could* be two bad GFCIs, but at that point I'd do more testing on the circuit). Does your license give you the power to dictate how other licensed professionals perform their business?
  62. #62
    You (as in the HI) DID the "evaluation", NOW the electrician has to do his testing to DETERMINE what the problem is.
    But it was funny...
    And your comment was like listening to Republicans say that they want SMALLER govmit ... the deciding that NEW LAWS must be made to make sure that everyone ELSE conforms to their thinking ... News flash! SMALLER govmit is LESS intrusion, not more intrusion. Those Republicans make Bill Clinton look like an angel.
    I wonder how those Republicans define "is" ... when they cannot even agree on what to agree or disagree on. just could miss replying to your remark, yeah, it's like ... sorry 'bout that.
    Mar 2008
    Charlotte NC
    No Jerry, I (as a HI) DETERMINED there was a problem (IT DON'T WORK RIGHT). It is the electricians job to EVALUATE the problem (FIGURE OUT WHAT'S WRONG)!
  64. #64
    Correct ... YOU "evaluated it" sufficiently enough to DETERMINE that there was a problem.
    Now the electrician needs to TEST IT in order to determine WHERE the problem is ... the problem which you found during your "evaluation" of it.
    YOU did as you were being paid to do - evaluate and report.
    Or are you admitting that you are not doing the job you are being paid to do?
    Mar 2008
    Charlotte NC
    Where exactly is "Evaluate" in DDID?