Old 04-14-2007, 08:33 PM
K Robertson's Avatar
K Robertson K Robertson is offline
Please help Identify This
Found this in a service panal today. Anyone have any idea what it is and can it be installed this way. It was tapped into the 60 amp A/C Breaker and grounded to the neutral bus. ??
The buyer said he thought it was some type of remote access devise.
Last edited by K Robertson : 04-14-2007 at 09:21 PM. Reason: more information added
Old 04-14-2007, 09:18 PM
paul hardy paul hardy is offline
Re: Please help Identify This
looks like a lightining arrestor and no it is not installed correctly most breakers only allow one wire under the terminal.
Old 04-14-2007, 11:24 PM
Tim Moreira's Avatar
Tim Moreira Tim Moreira is offline
Here's what I found in the 05 NEC:
Not exectally sure how or if it applies. Maybe Jerry can clarify this for us.
280.2 Definition.
Surge Arrester. A protective device for limiting surge voltages by discharging or bypassing surge current, and it also prevents continued flow of follow current while remaining capable of repeating these functions.
280.3 Number Required.
Where used at a point on a circuit, a surge arrester shall be connected to each ungrounded conductor. A single installation of such surge arresters shall be permitted to protect a number of interconnected circuits, provided that no circuit is exposed to surges while disconnected from the surge arresters.
230.82 Equipment Connected to the Supply Side of Service Disconnect.
Only the following equipment shall be permitted to be connected to the supply side of the service disconnecting means:
(3) Instrument transformers (current and voltage), high-impedance shunts, load management devices, and surge arresters.
Old 04-15-2007, 05:52 AM
John Arnold John Arnold is offline
Whatever it is, probably a surge device of some kind, it shouldn't be inside the panel enclosure.
Old 04-15-2007, 09:20 AM
Quote:
Right.