Originally Posted by
Jon Randolph
The rating that you give the service should be the smaller of the SEC, panel rating or main isconnect rating.
Except, as in this case, when there are multiple main disconnects, then the smaller of the service entrance conductor rating or the combined rating of the multiple mains. While multiple mains cannot be combined to get a true rating, they can be combined to get a 'maximum rating', and if that is smaller than the service entrance conductors, then that 'maximum rating' would be the service size, i.e., being the smaller of the two.
In the case stated above:
1/0 Copper Service Entrance Conductors
Service Equipment panel had 3 Breakers for means of main disconnect.
100A to house panel
30A to pool panel
60A to HVAC package unit panel
The 1/0 copper is rated for 175 amps, the 3 multiple mains add up to 190 amps, thus the service size is 175 amps.