Old 03-17-2008, 09:49 PM
mathew stouffer mathew stouffer is offline
Distribution Panels
Can I chalk this up to the electrician having a bad day? Does anyone know what the requirements are regarding securing wires entering panels. Is it 12 inches?
Old 03-18-2008, 04:42 AM
Richard Moore's Avatar
Richard Moore Richard Moore is offline
Re: Distribution Panels
Yep...NEC 334.30...within 12" of every cabinet, box, or fitting.
Richard Moore
Rest Assured Inspection Services - www.rainspect.com
Seattle, Washington
Old 03-18-2008, 07:05 AM
Brandon Chew Brandon Chew is offline
They also cannot jam so many cables into one clamp unless the clamp is listed for it. I believe two NM cables is the limit. Could someone confim and provide a source on that for me? tx.
Wahooo.... post #100 on the new board!
Old 03-18-2008, 12:48 PM
Plus ...
They are 'bundling or not maintaining spacing' for what looks like more than 24" for 'multi-conductor cables' too.
Derating in now required.
Old 03-18-2008, 01:13 PM
There were a few other problems not visible in the photo. Wrote it up as further evaluation by electrician to correct multiple installation insufficiencies.
  #6 (permalink)
Old 03-19-2008, 04:25 PM
Richard Abrams Richard Abrams is offline
Watch Bundling of romex cables as anything over 4 wires would have to be derated. Especially if insulation material is installed in these cavitys.
Arguing with an inspector is like wrestling a pig in the mud, pretty soon you realize the pig enjoys it.
  #7 (permalink)
Old 03-19-2008, 04:36 PM
Quote:
If even two NM cables (any multi-wire cable for that matter) are bundled or spacing was not maintained, then derating takes affect.
The code references "more than 3" but is also references "multi-conductor cables", because if you have 2 2-conductor cables (i.e., 2 multi-conductor cables), you have 4 conductors.
Derating then becomes
4-6 conductors - derate to 80%
7-9 conductors - derate to 70%
10-20 conductors - derate to 50%
21-30 conductors - derate to 45%
31-40 conductors - derate to 40%
41+ conductors - derate to 35%
  #8 (permalink)
Old 03-19-2008, 04:40 PM
Raymond Wand Raymond Wand is online now
Mathew,
At the top of the second picture are those cables going up into the return air duct?
The value of experience is not in seeing much, but in seeing wisely. - Sir William Osler 1905
Similar Threads
Wadsworth panels william siegel Electrical Systems: Home Inspection and Commercial Inspection 2 03-13-2008 06:18 AM
Zinsco panels Wendell Swedberg Electrical Systems: Home Inspection and Commercial Inspection 1 01-28-2008 06:10 PM
PVC as water distribution pipe Terry Beck Plumbing System: Home Inspection and Commercial Inspection 20 11-05-2007 07:09 PM
Best place/how to learn more about panels Ross Neag Electrical Systems: Home Inspection and Commercial Inspection 23 10-10-2007 02:00 PM
Distribution Panels Chip O'Brian Electrical Systems: Home Inspection and Commercial Inspection 5 07-23-2007 05:34 PM
vB.Sponsors
Ad Management by RedTyger