Old 04-21-2008, 09:19 AM
Michael Thomas's Avatar
Service and load side panels in close proximity
Service disconnect is in panel 4" to left of "load side" panel, bonded to same by conduit with ground wires to bushings at both ends (to the respective panels). Feeders run from 100A breaker at service panel to load side panel. Ground and neutral are not isolated at load side panel.
When the load side panel is in such close proximity to the service panel, and bonded in this manner, is it still considered a load side panel, or is it now part of the "service equipment" ?
Old 04-21-2008, 09:33 AM
Re: Service and load side panels in close proximity
Quote:
It is still "separate".
The dangers of the problem are now reduced to that conduit, but the load side panel is still "non-service equipment" and the neutral needs to be isolated from ground.
Old 04-21-2008, 10:08 AM
Thanks.
Similar Threads
non service equipment panels Jerome W. Young Electrical Systems: Home Inspection and Commercial Inspection 13 03-07-2008 10:11 AM
wiring service panels 101..(help Jerry P) Jim McClendon Electrical Systems: Home Inspection and Commercial Inspection 4 02-29-2008 04:25 AM
2 service panels, 1 ground Jon Randolph Electrical Systems: Home Inspection and Commercial Inspection 10 10-13-2007 08:42 PM
Load side panel close to service equipment Michael Thomas Electrical Systems: Home Inspection and Commercial Inspection 3 07-23-2007 09:39 PM