Old 08-06-2008, 02:53 PM
Richard Roshak Richard Roshak is offline
Water supply and panels
Is there not a code that prohibits this type of installation? Yes, that shut off valve has previously leaked directly onto the panel.
Rich
Home inspection
Old 08-06-2008, 03:41 PM
Billy Stephens's Avatar
Billy Stephens Billy Stephens is online now
Re: Water supply and panels
Quote:
Rich
Richard,
If you can document this area as being considered a wet location due to a previous event
NEC 312.2A would require the enclosure to be rated as water tight.
or
IRC. 2003 E3304.8 Energized parts guarded against accidental contact. Approved enclosures shall guard energized parts that are operating at 50 volts or more against accidental contact.
( If it is likely to get wet again and someone touches the energized dead front it would be considered accidental contact. )
If I were trying to stretch a code around Stupid.
But
I think I would write it as a Safety Hazard ( Location has a history of water being directly discharged onto the Electrical Panel. ) bla. bla. relocate ----.
Billy J. Stephens HI Service
Old 08-06-2008, 04:03 PM
Michael Thomas's Avatar
110.26(F)(1) (a) Dedicated Electrical Space. The space equal to the width and depth of the equipment and extending from the floor to a height of 1.8 m (6 ft) above the equipment or to the structural ceiling, whichever is lower, shall be dedicated to the electrical installation. No piping, ducts, leak protection apparatus, or other equipment foreign to the electrical installation shall be located in this zone.
Exception: Suspended ceilings with removable panels shall be permitted within the 1.8-m (6-ft) zone.
(b) Foreign Systems. The area above the dedicated space required by 110.26(F)(1)(a) shall be permitted to contain foreign systems, provided protection is installed to avoid damage to the electrical equipment from condensation, leaks, or breaks in such foreign systems.
(c) Sprinkler Protection. Sprinkler protection shall be permitted for the dedicated space where the piping complies with this section.
(d) Suspended Ceilings. A dropped, suspended, or similar ceiling that does not add strength to the building structure shall not be considered a structural ceiling.The piping is permitted within the electrical room but not within the dedicated equipment space directly above the electrical equipment. If leak protection is provided, the piping can be installed in the area above the dedicated equipment space.
This applies to panelboards
Old 08-06-2008, 04:22 PM
Quote:
Originally Posted by Michael Thomas View Post
110.26(F)(1) (a) Dedicated Electrical Space. The space equal to the width and depth of the equipment and extending from the floor to a height of 1.8 m (6 ft) above the equipment--
Thanks Michael,
Quick flip through Code Check did not show your reference.
CD versions are on the wish list.
* added pdf reference to Michael's correct code post
Last edited by Billy Stephens : 08-06-2008 at 05:15 PM. Reason: added reference pdf
Old 08-06-2008, 05:34 PM
Victor DaGraca's Avatar
Victor DaGraca Victor DaGraca is offline
An invaluable tool on CD starting at $30 (used) to $54 new
Amazon.com: Used and New: 2006 International Residential Code on CD-ROM
www.Home2Spec.com
  #6 (permalink)
Old 08-06-2008, 06:30 PM
Thanks,
Ooo I bet it has lots of pictures.
I'll have to check into NEC as well.
Now if only they had a Grand Pappy's Day like ( Mothers Day ) only for old smelly Guy's I'd be Set.
Home inspection
Similar Threads
Schedule 40 for water supply lines Jon mackay Plumbing System: Home Inspection and Commercial Inspection 2 06-24-2008 12:55 PM
water supply jeff boyle Plumbing System: Home Inspection and Commercial Inspection 13 10-12-2007 10:31 AM
Water heater supply lines Terry Beck Plumbing System: Home Inspection and Commercial Inspection 6 07-26-2007 05:17 PM
Water supply lines in attic dan orourke Plumbing System: Home Inspection and Commercial Inspection 1 07-14-2007 05:57 PM
PVC water supply lines in crawlspace Jeff Eastman Plumbing System: Home Inspection and Commercial Inspection 3 04-15-2007 08:56 AM
vB.Sponsors
Ad Management by RedTyger