Originally Posted by
Fritz Kelly
Maybe Scott is seeing something I'm not but it just looks like an ungrounded panel to me. I am not seeing any grounding conductors.
Jim Port
Is that the feed coming into the bottom of the panel? It looks like this is only a 3 wire feeder. Is this is a detached structure or attached.
If this was a detached structure with no metallic paths back to the other structure this may be ok. More details are neeed.
I'm with Fritz and Jim, and it's even worse than that.
Forget the "main panel" "subpanel" thing guys. If you would only forget that and think "Is this "service equipment" or is this "not service equipment", then other things would become apparent.
Jim point out part of it. There is no insulated neutral to that panel.
*IF* that is "service equipment", then those conductors coming up from the bottom are the "service entrance conductors", which means that the main disconnect would also be in this enclosure, and which also means that the uninsulated stranded copper serves as both the neutral and grounding conductors.
However, *IF* that is "not service equipment", then that becomes a feeder and that feeder neutral is required to be insulated (which it is not) and there is required to be a grounding conductor (which there is not)
Lanny,
Is that "service equipment" or is it "not service equipment"?
Therein lies your answer, and also answers whether those are "service entrance conductors" (neutral/ground may be combined as that is) or whether those are "feeder conductors" (which requires an insulated neutral).
I suspect that those are "feeders", meaning what needs to be done just got a whole lot more complicated and expensive.