Originally Posted by
Jim,
Nope, not "activate at 6 inches"
"The Six-Inch Rule. The photo eyes mentioned above
should not be installed higher than six inches above the garage floor. If the eyes are installed higher, a person or pet could get under the beam and not be detected by the photo eyes."
Thus the standard manufacturer's recommendation of 4" to 6" above the floor.
Which also meets the requirement stated in 16 CFR Part 1211:
(2) The obstruction noted in paragraph (a)(1) of this section shall
consist of a white vertical surface 6 inches (152 mm) high by 12 inches
(305 mm) long."
That 6" tall vertical surface used to set off the photo cells will trip anything 6 inches high *or less*. The manufacturer's 4" to 6" also meets that.