Old 09-12-2007, 04:48 PM
wayne soper's Avatar
Opinions
I would appreciate any opinions on this matter,
I recently got a call from a past customer who said there was a BIG problem with an oversight on my part and that the waste lines in her home had to be replaced. I asked her about the issue and she said that during an appointment with basment water proofing company the person saw water seeping out of the waste line and told her that her inspector shgould havce seen it and they have insurance and you should get him to pay.
She went right out, hired a plumber and had the line fixed before ever calling me.
I live right down the road and have been called many times to look at things and give advice during and after the inspection period. She knows I respond quickley.
I show up at the house and see the waste lines in the driveway. The lines look like many I have seen that were sitting in the dirt, white lines on pipe sides, dirt marks. They almost look like they were scraped off to look clean.
She says they were in the area above the entry to the crawl area which in most areas was less than 12 inches in height in most areas and was not accessible as noted in the report.
I ran the water for almost 2 hours in this home and inspected the crawl area last as far as I could get in and saw no leaks.
House was only used on weekends prior to sale.
I am wondering why I wasn't the first person she called as that is her normal routine. I'm sure you have all had a few clients that are like this and it's just part of the deal. You do and help out where you can.
But I wasn't the first called. She took no pictures of the damage prior to removal so I am suspecting that the damage was not visible to me at time of inspection but was buried.
The pipes are cracked to the point where there is no way a leak would not be found unless they were in the ground.
I'm just going over these things because I don't want to let her get away with something I firmly believe she is very capable of doing.
If I am wrong I admit it and make good, but Something smells fishy here.
Any thoughts would be appreciated. Thanks, Wayne
Old 09-12-2007, 04:57 PM
Gunnar Alquist's Avatar
Re: Opinions
Wayne,
Don't you love when someone says "the inspector should have seen that"?
If you use a contract, it should spell out what you can and cannot see (buried stuff, for instance). In addition, the contract should have some provision that requires that you be notified of a problem before corrective work is performed so that you can perform an evaluation. Either of these conditions would help to reduce your liability in this matter.
Depending on the price tag for the work, something like this would most likely go to small claims court. However, if the amount is great enough and she does sue you and goes after your insurance, it may do you no good as the insurance company may choose to settle out of court.
The apostrophe troll.
Old 09-12-2007, 05:09 PM
Re: Opinions
Yes my contract does state all those things and it would be small claims but my integrity and loyalty to my clients makes me second guess myself firstand them second, but the more i think about this, the fishier it smells.It's not the money. I can make more money. It is Whats the TRUTH and I can't determine that due to the fact that I was not given notice prior to repairs.
Old 09-12-2007, 05:14 PM
Billy Stephens's Avatar
Billy Stephens Billy Stephens is offline
Re: Opinions
Wayne,
I'd ask Her Don"t you have Home Owners?If yes won't they cover?
Deductible of Home Owners?
If she's had any drains that had to be cleaned? If yes receipts.
Name of basement water proofing company/Guy and receipts for the work done.
Name of Plumber/Company receipts of work done.
After all You/Insurance can"t consider the claim without knowing the cost.
How much time ago? Winter if they only used the home on the weekends did they freeze burst. Large group of people in the house and clogged the system filled with water.
May have $ in her eye's. Get all the information you can before it turns combative.
Billy J. Stephens HI Service
Old 09-12-2007, 05:18 PM
Rick Hurst's Avatar
Re: Opinions
Wayne,
Nearly every home inspector contract or agreement I've ever read has comments regarding that the HI should have the opportunity to inspect any item in need of repair prior to those repairs being done.
Then there's the catch phrase about in an emergency situation that repairs should be done to prevent any structural damages if needed.
That is where the problem lies for most.
Some plumber came out there and found a leak and pushed the repair as needing immediate attention.
No doubt, if it had been leaking severly you would have pick up on it.
You can take a old rusted out drain line as you have in that picture and whack it and cause those type of cracks to occur. Don't think it doesn't happen either.
Hold your ground and your checkbook tighter.
Rick
  #6 (permalink)
Old 09-12-2007, 05:26 PM
Re: Opinions
Wayne, you need to read her the "I'm not superman, I don't have x-ray vision clause" You know the one that tells her you can't see through dirt, walls, floors and such.
Mr. Inspector.net, Inc.
Allen, Texas 75002
  #7 (permalink)
Old 09-12-2007, 06:14 PM
Re: Opinions
Thanks guys, and rick that emergency thing is well taken but as I explained. This women called me very day for a week after the inspection to discuss items and I went to the house mumerous times as it is so close to my home. So why didn't I get a chance to see the damage before the repairs?
We'll see. Thanks for all of your opinions. Im sure you are all the same way and go over these things in your heads till you go nuts. We all make mistakes but a miss like this is in the "NO Way" category but I have to admit. Not impossible
  #8 (permalink)
Old 09-12-2007, 06:32 PM
Re: Opinions
Remember that, it is why you put it in the report!
Why was the guy there waterproofing? Did you report a moisture problem?
Why did she have time to call and get a second guy out to repair the problem but not to call you... especially if she wants you to pay for it?
Allen, Texas 75002
  #9 (permalink)
Old 09-12-2007, 08:24 PM
Nick Ostrowski Nick Ostrowski is offline
Re: Opinions
"This women called me every day for a week after the inspection to discuss items and I went to the house numerous times as it is so close to my home. So why didn't I get a chance to see the damage before the repairs?"
Sounds like the perfect question for this client Wayne. Why didn't she call you?
The bottom line is she screwed herself by calling you AFTER the work was done......that is if she ever had a case to begin with. Essentially, she altered everything. It's like you saying I hit your car when I pulled away in my car, you getting a new fender and paint job, and telling me after the "evidence" has been removed that I need to pay this bill. She's having "bill payers remorse" and is looking to hook you for the bill which ended being more than she expected.
Even if she were correct in her allegations against you and it was something you should have seen, how will you ever know? She had everything changed. Based upon your stated experiences with her following the initial inspection, she knew she could call you and you would have shown up as soon as possible. Why wouldn't she do so with something of this scale? Does she have any pictures of the defective pipes still in place prior to the work being done? My guess is no.
I'd stand ground Wayne.
  #10 (permalink)
Old 09-12-2007, 09:18 PM
Re: Opinions
Thanks Nick, No pics. Thats the first thing I asked her. I said. You aclled me every day for 2 weeks and now you don't call till after the work is done? Do you have pics. No why would I do that she said. We shall see. I'll let you all know the results and thanks again.
You guys are the best. It is a wonderful feeling to be a part of this forum knowing I can get honest opinons. Thank You all
  #11 (permalink)
Old 09-13-2007, 05:44 AM
Jon Randolph Jon Randolph is offline
Re: Opinions
I have a clause in my inspection agreement that I have 48 hours after notification to return to the home and evaluate the problem in person. No repairs can be performed prior to my evaluation. Once the repair has been made, you cannot evaluate the condition to either accept responsibility or explain that the scope of the inspection did not include that area due to access, being underground, behind walls, etc (hopefully you have written documentation of the limitations). If I am at fault and missed something I have no problem accepting responsibility and taking care of the problem.
Integrity Inspection Service, LLC
www.irsindy.com
(317) 345-1828
  #12 (permalink)
Old 09-14-2007, 07:30 AM
Stuart Brooks's Avatar
Stuart Brooks Stuart Brooks is offline
Re: Opinions
What damages and/or losses did the client incur as a result of the supposed missed cracked waste lines during inspection? Whether you missed the cracked lines or not, you did not cause damage to the lines. The lines would need to be replaced regardless of the inspection. Was her crawl space contaminated with waste water? You possibly could be held responsible for cleanup or other damages due to the waste lines failing.
I agree that the client should have called you as soon as the condition was found. Even if it was an emergency, it would have been preferrable to be notified immediately after the call to the plumber.
Besides the X-ray vision, can't-kick-holes-in-walls things, I tell the client right up front that I am not perfect. Any one inspector will, in all probablity, not see something that another inspector would find if he came in right behind. And, I would probably have something listed that the other inspector would not see.
  #13 (permalink)
Old 09-14-2007, 07:46 AM
Ken Amelin Ken Amelin is offline
Re: Opinions
Wayne,
The owner made a mistake by not contacting you, but if I understand correctly you're trying to determine if it you missed it and if it was your fault.
I would ask the owner to provide you with the name and number of the contractor who fixed it and call them. Ask where the faulty pipe was found during their repair. I would say this third party is the deciding witness. "Whatever they say is how you pay"
  #14 (permalink)
Old 09-14-2007, 02:59 PM
Bruce King Bruce King is offline
Re: Opinions
Was the house at least 40-50 years old?
I report on every one of these with cast iron or orangeburg (fiber) pipes that they will have deteriortion present inside and will get worse and have to be replaced.
The cracks were against the ground no doubt and partially sealed with gunk, that is why you did not notice the ground wet around them.
  #15 (permalink)
Old 09-14-2007, 03:37 PM
Re: Opinions
"I would ask the owner to provide you with the name and number of the contractor who fixed it and call them. Ask where the faulty pipe was found during their repair. I would say this third party is the deciding witness. "Whatever they say is how you pay"".
I wouldn't be so quick to jump on board with that. It seems well and good but you have no idea what that plumber's relationship is with the client (ie - friend, family member) and that relationship could sway the plumber to paint a more favorable picture for the client in hopes of getting Wayne to pay for everything.
Wayne, if you feel responsible enough to step outside the boundaries of the verbiage in your inspection agreement, your inspection report, and any supporting pictures and still take some or all responsiblity for the repairs, that is your choice. Otherwise, it sounds as though you have plenty of backup to stick to your guns on this if you feel the defect was not where she says or if it was not observable.
  #16 (permalink)
Old 09-14-2007, 04:10 PM
Re: Opinions
What if the guy who "found" the problem (water proofing guy) is friends with the plumber who got to dig this buried mess out for $$$
  #17 (permalink)
Old 09-14-2007, 04:50 PM
Re: Opinions
Wayne,
Sometimes we're right, sometimes we're wrong, sometimes we pay. It's should end up as a business decision, not an ego decision.
In my opinion, This thread appears to be very defensive. It appears like the comments I see here are trying to get the inspector off the hook and not thinking about reality, or giving the other party any credence.
If I were the abritrator in this case, I would listen to the parties involved and the testiment of the contractor who fixed it. If the third party witness (the contractor who fixed the problem) says it was a visible defect, I would go with the witness.
Sometimes it doesn't matter who is right or wrong. Sometimes it is best to negotiate a settlement. It's about money. That's it.
So Wayne, My suggestion is to contact the third party contractor, ask them what the problem was and either use the information in defense, or negotiate a settlement.
It's that simple. Don't loose any sleep over it. get on with it. If you get too defensive you get a lot of bad publicity, and you will still loose money. If you settle based on the weighted evidence (third party comments), it will still cost money, but the people will be happy, you will get kudo's and more referals.
Besides, negotiated settlements usually end up costing you less money than a defensive approach.
Good luck!
  #18 (permalink)
Old 09-14-2007, 05:12 PM
Re: Opinions
Those kind of referrals I could do without.
  #19 (permalink)
Old 09-14-2007, 06:26 PM
Re: Opinions
Yeah Ken, You are right. All I am doing is asking for reciepts, photos, before and after and descriptions from the contractors. That doesen't seem unfair to me. Sometimes a payoff with a release of liability is worth its weight in gold for a certain type of customer.
  #20 (permalink)
Old 09-14-2007, 08:41 PM
Carol Perkins Carol Perkins is offline
Re: Opinions
I just paid to replace part of a floor in the living room. There was no structural problem just a hump that we failed to note in our report. I chose to have the work done even though I did not feel it was justified for several reasons: 1. Customer satifaction, 2. Realtor relations, 3. Company reputation, 4.my piece of mind (I don't do stress well) 5. cheaper than my deductable on E&O 6. no lost time in court or arbitration. My point is I had to decide what was more valuable to me - winning the point or keeping my reputation.
Try talking to her, get the information mentioned above, tell her your position, and try to negotiate a reasonable settlement. Get her to sign a "no plublishing"
agreement afterwards. Helps if you have a disinterested third party involved also.
The last time I talked to the customer she was very happy and willing to send friends to us.
