Results 1 to 3 of 3
    Alan C Grubb's Avatar
    Alan C Grubb Guest
    Default Fire Place Chimney No Fire Break
    Inspected home recently that had no metal fire break between attic and second floor. Home was built back in seventies. Called it for repair. Not sure of code, was this correct? Would post picture but I keep getting html code question.
    A.D. Miller's Avatar
    A.D. Miller Guest
    Default Re: Fire Place Chimney No Fire Break
    Quote Originally Posted by Alan C Grubb View Post
    AG: You were correct. It does not necessarily need to be metal, but it does need to be firestopped.
    R602.8 Fireblocking required.
    Fireblocking shall be provided
    to cut off all concealed draft openings (both vertical and horizontal)
    and to form an effective fire barrier between stories, and
    between a top story and the roof space. Fireblocking shall be
    provided inwood-frame construction in the following locations.
    1. In concealed spaces of stud walls and partitions, including
    furred spaces and parallel rows of studs or staggered
    studs; as follows:
    1.1. Vertically at the ceiling and floor levels.
    1.2. Horizontally at intervals not exceeding 10 feet
    (3048 mm).
    2. At all interconnections between concealed vertical and
    horizontal spaces such as occur at soffits, drop ceilings
    and cove ceilings.
    3. In concealed spaces between stair stringers at the top and
    bottom of the run. Enclosed spaces under stairs shall
    comply with Section R311.2.2.
    4. At openings around vents, pipes, ducts, cables and wires
    at ceiling and floor level, with an approved material to
    resist the free passage of flame and products of combustion.
    5. For the fireblocking of chimneys and fireplaces, see Section
    R1003.19.
    6. Fireblocking of cornices of a two-family dwelling is
    required at the line of dwelling unit separation.
    I write them up, but it's standard in my area to not have any fire stop/ blocking in houses built in the 70's.