    mathew stouffer's Avatar
    mathew stouffer Guest
    Default Vent clearance to roof
    This is for a gas snow melt boiler. The tag was difficult to read but it appeared to be a simpson Dura Vent. Does this require 2 ft of clearance above the roof.
    Chicago
    Default Re: Vent clearance to roof
    Duravent does not recommend outside vents in cold climates unless installed in an enclosure. Once that is done I'd just follow their height termination chart.
    http://home.comcast.net/~marylandhom...BVentGuide.pdf
    Check out Fig. 11, page 8.
    Connecticut
    Jun 2010
    San Luis Obispo
    "appeared to be a simpson Dura Vent" Simpson "B-Vent"? or Direct Vent? I can't tell from the picture.
    Does the "boiler" manual call out clearences for it's venting?
    Also it needs a wall strap above that 90, as the leg with the cap could rotate 180 and face the cap down (bad).
    My2c
    Cool Re: Vent clearance to roof
    Cross-check the appliance and vent listed instructions and go with the most restrictive as always.
    Yes, that vent needs support both below the elbow to provide support for that horizontal leg and as Stephen pointed out above it. However, if you only have one point of stability, so the vent could wave at you as you drive by and sag. You cannot rely on the listed wall penetration, which is not visible but hopefully they used.
    Note that since you are in snow country a case could be made to extend that vent well above the roof and put a 'cowcatcher' snow diverter on the roof immediately uphil from it.