Results 1 to 16 of 16
Thread: gas water heater vent terminatin
12-01-2007, 04:07 PM #1
Gas water heater vent termination
Can anyone tell me if this is proper vent termination? (gas water heater)
Similar Threads:Last edited by Zibby Swieca; 12-01-2007 at 06:13 PM.
12-01-2007, 04:46 PM #2
Re: gas water heater vent terminatin
Zibby,
Looking at IRC 2003 G2427.8 Venting system termination location.
The minimum clearance from any opening into a building is 6 inches and the distance goes up with the Btu rating of the appliance.
12-02-2007, 09:23 AM #3
Re: Gas water heater vent termination
12-02-2007, 10:11 AM #4
edited
12-02-2007, 10:36 AM #5
Scott,
IRC 2003 G 2427.8(503.8) Section 3
Direct Vent 10,000 Btu at least 6 inches from any air opening into a building
over 10,000 Btu but not over 50,000 Btu shall be installed with a 9 inch vent
termination clearance
over 50,000 Btu shall ave at least a 12 inch vent termination clearance.
Zibby,
T&P discharge line is improper.
12-02-2007, 10:45 AM #6
edited
12-02-2007, 10:54 AM #7
Thanks,
It is 40.000 Btu
12-02-2007, 11:10 AM #8
12-02-2007, 11:41 AM #9
Zibby,
Depends on what part of the wiring is aluminum. If the conductors are the larger size for electric appliances or other panels, then AL is fine. If it is for the branch circuits, then there is a potential problem and corrections should be designed and implemented by a licensed electrical contractor.
12-02-2007, 11:55 AM #10
Yes it is for the branch circuits.
12-02-2007, 11:56 AM #11
Check the manufacturer's instructions - I've been surprised more than once at the the small separation some require from potential means of air entry to a structure.
12-02-2007, 12:21 PM #12
12-02-2007, 01:00 PM #13
Personally I don't care for the Alum Wire verbiage. I like telling my client this "This home has single strand aluminium branch circuit wiring. Although many homes have this type of wire and show no signs of problems it is considered to be a fire hazard and it should be replaced. Some repair options are available but they have been proven to have problems as well. Have a qualified electrician provide a quote for replacement of all aluminium branch circuits."
As for the water heater:
That is not a direct vent.
The vent termination is wrong.
The TPR line is wrong.
12-02-2007, 01:17 PM #14
edited
12-02-2007, 01:25 PM #15
12-02-2007, 07:01 PM #16
Re: gas water heater vent termination