Results 1 to 9 of 9
Thread: Wood contact
    Jim Gecz's Avatar
    Jim Gecz Guest
    Default Wood contact
    I would be interested in my fellow inspector's report verbiage for wood in direct contact with a fireplace chimney structure (as seen in the attic.). Besides calling for a level II, how would you report this?
    For any inspectors (Bob and any other FIRE certified guys) who conduct Level II’s how would you report this, especially if you discovered the terra cotta liner shown in the second photo?
    The reason I ask is a number of NJ chimney sweeps do not consider either condition a problem.
    Cool Re: Wood contact
    Jim, I think your only answer as a Home Inspector would be to either perform a full level II or recommend one by a qualified inspector. You may point to the conditions you observed as grounds for the recommendation but I would not get into a partial inspection. Since a Level II is indicated for the sale or transfer of property, you do not need findings to support that recommendation. Report what is within the scope of your inspection as a home inspector but do not go beyond that unless you go all the way.
    As for these conditions being acceptable, that is an indefensible position. An ethical inspector does not proclaim anything as "safe" or "acceptable". He simply states observable facts and puts them into context of published standards. Proclamations of suitability are engineering decisions. If you are not a licensed professional engineer, stick to the facts and let them speak for themselves.
    As for dating, clearances and liners required date back to the 1927 Uniform Building Code so if the home was built before then, there stands a good chance it did not meet the code when built. Just because the defects you've shown here are also present in most homes in the US does not minimize their importance.
    You can state whether or not a defect fails to meet a current code or standard without having to conduct research on the code history in that jurisdiction. You are not in court proving a negligence on a construction defect but simply using current knowledge to ascertain what is acceptable practice or not. Wether or not they knew it at the time of construction, we now know lack of clearance, insulation encroaching into stated clearances, breaches in mortar joints are all defects as identified by current codes and standards. Those codes and standards are responsible for making the point as to what the hazard is and why it is in the code.
    -Just back from HPBA EXPO. Dale made two great presentations and was a major presence at the HPBA Technical Cmte. meeting on Wed.
    HTH,
    Bob
    Jim Gecz's Avatar
    Jim Gecz Guest
    Default Re: Wood contact
    Thanks for the great feedback, Bob. You are always the pro.
    Jim
    Kevin Stewart's Avatar
    Kevin Stewart Guest
    Jim
    To answer your question, "Bob did not extrapolate the question from the original so he never got round to answering it. (some Bob speak)"
    When I see wood against a chimney like this my verbiage goes something like this. 'wood framing around the chimney structure does not meet clearance to combustibles standards', code requires clearance to combustibles around chimneys as this is a potential fire hazard, I am unclear of the first mention of this in a code book but I am fairly sure these clearance issues go back to the 1920's.
    Kevin
    Jon Randolph's Avatar
    Jon Randolph Guest
    What would be the clearance for a masonry lined chimney chase? The way I look at it, there is at least 8" between that flue and the wood in that picture (if it is unlined), since it is lined, that adds another inch or so to the distance. Unless there are issues with the mortar joints, I have not been calling that out.
    Is there a clearance for that installation?
    It does appear that the terra cotta lining is spalling, (indicative of excessive moisture) so I would call it out to be re-lined possibly in need of a crown and/or rain cap.
    Jon, the clearance is to the outside of the chimney proper--not the flue lining. A "chase" is essentially a housing for something else such as a factory chimney, cables, pipes, etc. If over 4 stories, it is considered a "shaft", which must be fire rated construction.
    Spalling of a flue can be caused by many things. I suggest you take Dale Feb's course so you can distinguish btw them and how to report them. If you comment on the flue condition then you should be doing a full Level II inspection or at least recommending one.
    The clearances to combustibles are clearly stated in the building codes so I would direct you there for starters.
    HTH,
    Bob
    Jon, the clearance is to the outside of the chimney proper--Bob
    Bob,
    Please define "outside of the chimney proper".
    I've seen some with huge masonry walls, long, tall, and wide, in which a fireplace and chimney were only one small part of that large and massive masonry structure.
    Wood furring strips on the CMU.
    On something like that, what is considered "the chimney proper" and what is "outside of" that?
    Healdsburg, CA
    Chimney fire-stopping details.
    PS: I would automatically recommend a NFPA Level II inspection of all fireplace chimneys before the close of escrow and transfer of title.
    Also, FWIW - if I where king I’d outlaw the building of all masonry fireplace chimneys in California or any seismically impaired area in the US as they’re both dirty and dangerous.
    JP, in the case where the exterior wall of the house is flush with the chimney, the point where the chimney's sides meet would be the limit of the clearance applying--not the length of the whole wall.
    I see wood furring strips on chimneys all the time and I see ungrouted CMUs all the time. Still wrong.
    I tend to agree with Jerry M. esp. with regards to seismic country. After seeing Dale's photos and the Rampart General precast fireplace he has in his shop, I don't see how you could leave a full masonry Fp in a home after a seismic event. Those factory chimney conversions are very wishy-washy with regards to how to anchor them and, to my knowledge, no one has tested any anchoring system such as Tapcon screws to seismic requirements. The current building codes call for the bond beam to be tied into the building. This is to delay the collapse of the chimney sufficiently so the occupants can escape without being crushed. Something to think about. The problem with Calif. is, you can have Dale himself inspect a chimney and have a seismic event or mud slide damage the chimney before he gets to the office and writes up his report. Inspections are a snapshot in time.
    Not only have I never seen a single code compliant chimney, I don't know anyone who has ever seen one that meets 100% of the code unless Dale is holding out on me.
    Bob
