Re: Pro-Flex gas line support
I don't see anything in the Gastite manual, or any of the manuals, not even the ProFlex CSST manual, which requires installation in concealed areas.
They all do state, however, that for concealed installation, special care and protection is to be made for protection against physical damage.
That said, though, the exposed section running across the floor is, obviously, exposed to physical damage would need to be protected from same. That would be done by installation of running boards on both sides, which, of course, would create another problem: a trip hazard.
Then there is the proper support for the CSST piping, which could be done by supporting to the protective running boards which are installed and which are now trip hazards.
In the ProFlex installation manual, 4.0 Installation/Practices Guidelines, at 20., states: "Along Side of a structure: When installed along the outside of a structure (between the ground and height of 6 ft) in an exposed condition, the CSST shall be protected from mechanical damage inside a conduit or chase. A conduit or chase is not required if the tubing is installed in a location that will not subject the CSST to mechanical damage."
That, to me, would also apply to interior exposed locations where exposed to physical (mechanical) damage.
The above is repeated in 4.3 Routing, c) Along side a structure.
What I did not see in there which is in the other manuals such as Gastite, and I only skimmed through the ProFlex manual, was the requirement that all ends of the CSST be terminated into a proper fitting which is rigidly mounted, but it is in the other manuals so it is likely in this manual - which means that the CSST could not go directly to a flexible appliance connector, there is required to be a rigidly mounted and approved fitting at the end of the CSST.
Thus, no matter how you look at it, that installation would be wrong.