07-15-2007, 07:55 PM
Direct Vent Located Below Bedroom Window
I could not find anything specifically prohibiting locating a direct vent below an operable window. Can anyone tell me if this arrangement is OK?
The fireplace is a pre-fab Heat-N-Glo model SL-750TR-C with gas logs. The direct vent is located about 3' below and slightly over from an operable bedroom window.
Bruce Breedlove
www.avaloninspection.com
07-15-2007, 10:14 PM
Re: Direct Vent Located Below Bedroom Window
The listed clearance requirement is 12 inches.
See page 36 of the SL750 Install Guide:
07-15-2007, 10:26 PM
Thanks, Dom. I guess I should have tried a bit harder to find that info.
Bruce Breedlove
07-15-2007, 10:58 PM
clearance is fine. However, the way they installed that trap cap is not. It was installed after the siding instead of being installed against the sheathing. This will eventually leak. You should recommend it be cut into the siding and caulked on 3 sides leaving the bottom open to drain against the drainage plane. There is a flange along the top of the base pan that must be hooked up under the housewrap.
Was this unit added on after initial construction? Appears so. However, sometimes during construction, the siding monkeys will pull the termination then reinstall it upside down. They also love to lower their pump jacks onto it ripping them off the wall.
FYI- on HHT terminations, clearances are measured from the trapezoid portion and not the base pan itself.
HTH
Bob
07-16-2007, 03:40 PM
Bob,
The direct vent was installed during original construction. The house was built in 2004. There was evidence of repairs around and below the direct vent (additional nails in siding and paint touched up). There was also evidence of a leak at the ceiling of the garage just inside the exterior wall and below the horizontal run of the metal chimney (water stains and small drain holes poked through drywall ceiling).
From what you are saying their repairs were not done correctly. I'll let my client know. Thanks for your input.
Bruce Breedlove
07-16-2007, 03:53 PM
In my area this is not proper as the vent of a gas fired unit must be at least 4' from any window or opening. As you stated it was only 3' from the window. I would write this up as improper clearences as per local gas company's requirements.
The installation instructions may state that it is OK but local "codes" superseed the installation insturctions on the venting. I should say local gas companys regulations require the 4' clearences.
Well thats my 2 cents.
Brian Kelly
Kelly Home Inspections
07-16-2007, 04:18 PM
I also thought it was 4', but this is what the 2003 IRC says:
M1804.2.6 Mechanical draft systems. Mechanical draft
systems shall be installed in accordance with their listing,
the manufacturer’s installation instructions and, except for
direct vent appliances, the following requirements:
1. The vent terminal shall be located not less than 3 feet
(914 mm) above a forced air inlet located within 10
feet (3048 mm).
2. The vent terminal shall be located not less than 4 feet
(1219 mm) below, 4 feet (1219 mm) horizontally
from, or 1 foot (305 mm) above any door, window or
gravity air inlet into a dwelling.
Ah, I see you are talking about a local gas company's code, nevermind.
Reason: Misread earlier post
07-16-2007, 05:03 PM
Brian, double check that local ordinance. Make sure it isn't just a mis-interpretation as Fritz pointed out. Direct vents are listed and do not follow the code section on mechanical draft systems.
So Bruce, was this installed by the huge local HHT distributor?? I spent a week with them last Spring working our way out from Denver to Castle Rock. Roasted around noon then finished up in a blizzard that same afternoon. Interesting weather you have!
I'll bet the installer did install this termination originally only to be removed by the siding guys. Then, they sent a guy back out to slap it up against the side of the house and nuke it with caulk. This WILL eventually leak.
| Thread Tools |
Search this Thread |
| Thread |
Thread Starter |
Forum |
Replies |
Last Post |
| Electrical service box located in closet |
Kevin Luce |
17 |
05-28-2008 08:40 PM |
| Gas fireplace direct vent location |
Jon mackay |
Fireplaces, Chimneys and Solid Fuel Burning Appliances: Home Inspection and Commercial Inspection |
14 |
07-11-2007 07:16 PM |
| B Vent Window Clearance |
Jim Robinson |
9 |
06-16-2007 09:11 AM |
| Gray PVC for direct vent furnace |
Jon mackay |
0 |
06-08-2007 05:52 AM |
| LP tank near direct vent |
Frank Bombardiere |
1 |
05-22-2007 07:11 PM |