Old 06-11-2008, 11:35 AM
Greg Frazier Greg Frazier is offline
Water heater venting
I inspected a house with an unlined chimney with two separate flues. Each flue had a cleanout door. The water heater vented into the left flue and was backdrafting badly. The vent connector rise was less than 6 inches as required by the manufactures installation manual. Whirlpool manual says "CAUTION VENT CONNECTORS MAY NOT TERMINATE WITHIN A CHIMNEY
FLUE SERVING A FIREPLACE UNLESS THE FLUE OPENING IS PERMANENTLY SEALED." Does this mean the cleanout door must be sealed as well as the chimney opening where the vent connector enters? By the way, the cleanout door can't be sealed right now anyway. It is propped open by a gas line tapped from the water heater going up to a gas log. There were other problems as well.
Old 06-12-2008, 06:51 PM
Eric Barker's Avatar
Eric Barker Eric Barker is offline
Re: Water heater venting
Two flues, a fireplace and water heater. Is there something that makes you think that the water heater is venting into the fireplace flue? The clean out is generally for the fireplace only and should be kept closed to permit proper drafting for what ever is using using the flue.
In any event, any unlined flue needs evaluation.
Eric Barker
Barrington, IL
Old 06-13-2008, 09:44 AM
Dana Bostick's Avatar
Dana Bostick Dana Bostick is offline
It's always been my understanding the gas appliances should not ever be vented into unlined chimney flues due to the fact that the exhaust from them contains a lot of moisture which, in combination with the soot etc., can become acidic and deteriorate the chimney and mortar.
"Political Correctness is a doctrine, fostered by a delusional, liberal minority and rabidly promoted by an mainstream media,which holds forth the proposition that it is entirely possible to pick up a turd by the clean end."
Old 06-13-2008, 09:46 AM
Bob Harper's Avatar
That reference means they recognize you can use any flue for venting as long as it meets the requirements for that appliance and the other code sections. Therefore, in order to vent a water heater or furnace into a fireplace flue, you would have to permanently block off the fireplace from the flue. The WH would then have to vent directly into the first flue tile. However, you still need at least 12" of flue to extend below the breech connection, which means the smoke chamber. You need access into the smoke chamber to inspect and clean out debris. The flue also would need to be inspected for suitability for that application (Level II). Since fireplace flues are generally much too large for heaters, it would require a listed liner regardless. If you still wanted to do this, you would have to remove the vented gas logs.
HTH,
Bob
Similar Threads
gas water heater Jerome W. Young Fireplaces, Chimneys and Solid Fuel Burning Appliances: Home Inspection and Commercial Inspection 25 07-19-2008 11:12 AM
Tankless Water Venting Mike Oliver Plumbing System: Home Inspection and Commercial Inspection 3 12-28-2007 04:52 PM