Results 1 to 12 of 12
Thread: Proof read this
11-15-2011, 07:43 AM #1
Proof read this
These are 2 documents I wrote for my backflow testing service.
If you would, proof read them and offer suggestions and advice.
I wanted you (HIs from IN) to proof read them because many of you (myself included) are so anal (not an insult).
Thank you
The Georgia Environmental Protection Division (EPD), and the Columbus Water Works require backflow prevention assemblies be serviced and maintained in accordance with the manufacturers instructions. To insure that backflow prevention assemblies are performing to the manufactures standards, the water consumer is required to have backflow prevention assemblies tested annually by a Georgia state certified Backflow Prevention Assembly Tester (BPAT). Backflow prevention assemblies not performing to the minimum standards of the manufacture must be serviced or repaired as needed. After any service or repair is made to a backflow prevention assembly, the assembly must be re-tested and a report of the service or repairs made including test results, filed with the water authority by the tester.
The backflow prevention assembly listed below did not meet minimum standards as required by the Georgia Environmental Protection Division and the Columbus Water Works.
Test results and a description of the service or repair that is likely needed is provided for your benefit.
Location; .
Manufacturer; Model; , Size; , Serial #; , Date of test;
Check valve #1,
Check valve #2,
Other,
The backflow assembly needs to be disassembled, cleaned, and examined to determine if any parts need to be replaced.
Dissolved minerals in the water will build up on internal parts of the assembly. Over time this buildup will cause the internal seals to “Foul” or leak. When these seals leak, the assembly will not function properly.
Often, just disassembling and cleaning of the backflow assembly will restore the assembly to acceptable standards. Fouling of the seals is the most common reason that a backflow assembly fails the annual test.
Disassembling and cleaning the backflow assembly is a fairly straightforward task, and can be performed by most maintenance staff in about 2 hours. If you do not have a maintenance person you can use an ordinary plumber.
You do not need a certification to service or make repairs to a backflow assembly, only for testing.
I will be happy to provide your maintenance person with instructions and advice on how to perform the service, at no charge. After the service has been performed, I will retest the assembly, again at no charge.
Thank you
Rick Cantrell
Backflow Testing of Columbus
912 42nd st
Columbus GA 31904
706 221 1495
Why do I need to test the backflow assembly?
Yearly testing assures that all backflow assembles are performing to standards that help protect everyone connected to the municipal water supply. Without backflow prevention and regular testing, your neighbor could be polluting your drinking water.
Clean water, like clean air, is something we can live with.
My plumber said he can test my backflow assembly, and if it needs service, he can do that also. Why should I use your service?
It is a conflict of interest for the backflow tester to also make repairs to the backflow assembly. There is a financial incentive to find backflow assemblies that “need to be repaired”. To make matters even worse, the person that made the repairs then certifies that the repairs they made, were performed correctly.
There is a better way. Use an independent 3rd party tester that does not do repairs. When service is needed, use the same 3rd party tester to test the backflow assembly after service is performed. This is not only the best method, but the only way to insure you are not spending money on unnecessary repairs and the repairs were properly performed.
I perform backflow testing. I do not perform backflow repairs. I have no reason to report that repairs are needed if they are not in fact needed. When service is needed, you choose who does the service. I then retest the backflow assembly to certify that the assembly is functioning properly. There may be a small trip charge, but there is no charge for the second test.
Similar Threads:Last edited by Rick Cantrell; 11-15-2011 at 05:18 PM.
11-15-2011, 09:31 AM #2
Re: Proof read this
Wow. Too many words. Cut it down by 50% and you might have something.
11-15-2011, 09:53 AM #3
11-15-2011, 10:41 AM #4
Re: Proof read this
Sorry to pile on, but, I almost didnt want to read it. Edit half of that at least. Change the font. Add some white spaces between the text.
Speaking as a licensed auto mechanic; consider changing that analogy between emmisions and the backflow preventer. I didn't make the similarity between the two...
Good luck with your new venture,
Steve
11-15-2011, 11:02 AM #5
11-15-2011, 03:55 PM #6
Re: Proof read this
Rick
On the first document. I don't think the analogy of the vehicle emissions works either. I would lose that paragraph and just try to stick to the point.
On the service document in the first paragraph you use manufactures, should read manufacturers.
11-15-2011, 04:58 PM #7
Re: Proof read this
Thanks guys
Changes have been made
11-18-2011, 04:00 AM #8
Re: Proof read this
Here is some language for the beginning of your letter.
Backflow is the reversal of the normal and intended direction of water flow in a water system. Devices and assemblies known as backflow preventers are installed to prevent backflow, which can contaminate potable water supplies.
Why is backflow a problem?
Backflow is a potential problem in a water system because it can spread contaminated water back through a distribution system. For example, backflow at uncontrolled cross connections (cross-connections are any actual or potential connection between the public water supply and a source of contamination or pollution) can allow pollutants or contaminants to enter the potable water system. Sickness can result from ingesting water that has been contaminated due to backflow.
Backflow may occur under the following two conditions:back-pressure:
Back-pressure is the reverse from normal flow direction within a piping system as the result of the downstream pressure being higher than the supply pressure. This reduction in supply pressure occurs whenever the amount of water being used exceeds the amount of water being supplied (such as during water-line flushing, fire-fighting, or breaks in water mains).
back-siphonage: Back-siphonage is the reverse from normal flow direction within a piping system that is caused by negative pressure in the supply piping (i.e., the reversal of normal flow in a system caused by a vacuum or partial vacuum within the water supply piping). Back-siphonage can occur when there is a high velocity in a pipe line, when there is a line repair or break that is lower than a service point, or when there is lowered main pressure due to high-water withdrawal rate (such as during fire-fighting or water-main flushing).
12-26-2011, 09:36 PM #9
Re: Proof read this
A well-written article! My suggestions are in red. I added a space (to make two spaces) between the end of a sentence and the beginning of the next, but because I had to copy and paste, they may have already been there. My word processor sometimes does that. So, of course, these won't show in red. The red underlines are not mine; spellcheckers don't like some of the technical words that we use.
Some of my additions are small and may be hard to see, e.g., manufacturer's (possessive - one manufacturer) vs manufacturers (plural):
The Georgia Environmental Protection Division (EPD), and the Columbus Water Works require backflow prevention assemblies be serviced and maintained in accordance with the manufacturer’s instructions. To insure that backflow prevention assemblies are performing to the manufacturer’s standards, the water consumer is required to have backflow prevention assemblies tested annually by a Georgia state certified Backflow Prevention Assembly Tester (BPAT). Backflow prevention assemblies not performing to the minimum standards of the manufacturer must be serviced or repaired as needed. After any service or repair is made to a backflow prevention assembly, the assembly must be re-tested and a report of the service or repairs made, including test results, filed with the water authority by the tester.
The backflow prevention assembly listed below did not meet minimum standards as required by the Georgia Environmental Protection Division and the Columbus Water Works. Test results and a description of the service or repair that is likely needed is provided for your benefit.
Location; .
Check valve #1,
Check valve #2,
Other,
Dissolved minerals in the water will build up on internal parts of the assembly. Over time this buildup will cause the internal seals to “Foul” or leak. When these seals leak, the assembly will not function properly. Often, just disassembling and cleaning of the backflow assembly will restore the assembly to acceptable standards. Fouling of the seals is the most common reason that a backflow assembly fails the annual test.
Disassembling and cleaning the backflow assembly is a fairly straight-forward task, and can be performed by most maintenance staff in about two hours. If you do not have a maintenance person you can use an ordinary plumber. You do not need a certification to service or make repairs to a backflow assembly, only for testing.
Thank you
Rick Cantrell
912 42nd St
Columbus GA 31904
706 221 1495
Q: Why do I need to test the backflow assembly?
A: Yearly testing assures that all backflow assembles are performing to standards that help protect everyone connected to the municipal water supply. Without backflow prevention and regular testing, your neighbor could be polluting your drinking water. Clean water, like clean air, is something we can live with.
Q: My plumber said he can test my backflow assembly, and if it needs service, he can do that also. Why should I use your service?
A: It is a conflict of interest for the backflow tester to also make repairs to the backflow assembly. There is a financial incentive to find backflow assemblies that “need to be repaired”. To make matters even worse, the person that made the repairs then certifies that the repairs they made, were performed correctly.
12-27-2011, 05:33 AM #10
Re: Proof read this
Thanks Garrett
12-27-2011, 10:55 AM #11
12-27-2011, 11:40 AM #12