Results 1 to 13 of 13
Thread: Thermostat location?
05-21-2007, 07:14 AM #1
How will this location, within 3' of the thermostat, in relation to the return air affect the equipment function?
Similar Threads:badair http://www.adairinspection.com Garland, TX 75042 TREC # 4563
05-21-2007, 07:18 AM #2
Re: Thermostat location?
The thermostat will get a false reading as the air moves across the stat to the return air grill.
05-21-2007, 08:22 AM #3
Maybe I misunderstood an HVAC technician who is very reputable in this area, but I swear he said to me it was good to have the thermostat "near" one of the return vents. In my house that is the case with both my HVAC systems.
05-21-2007, 09:04 AM #4
It should make the temperature reading more representative of the actual air temperature in the house. The thermostat is not sitting in a dead-air pocket.
Why? There is a misconception that airflow cools objects. This is true if either the object is warmer than the air or if it is moist. If the object is dry, airflow tends to bring the object to air temperature, which, for a thermostat, is a good thing. (Of course, if the air is moving really fast, the object will be heated, think of reentry from outer space.)
I would agree.
- BOB
05-21-2007, 09:35 AM #5
Ditto, Bob.
You don't want the SUPPLY air to blow across the stat, but a stat mounted on the wall near a return grill is a good thing.
05-21-2007, 10:37 AM #6
Right. The temperature of the air going into the return register is (likely) representative of the temperature of the air in the house. The temperature of the air coming out of a supply register is more representative of .. well.. the temperature of the heat exchanger. (Of course there is some temperature drop in the supply ducts.)
- BOB
05-21-2007, 11:46 AM #7
All I can say is when I took the Manual D duct school we were told not to place the thermostat near either the sully and or return air registers as it would possiable give it a false reading. I have never put a stat near either.
05-21-2007, 11:57 AM #8
Not a thing wrong with that location, in fact it is a good location. As for a false reading, it is reading the air temp. The air at the return will be more representative of the air in the home, as the air is being pulled to the area from around the home.
05-21-2007, 01:39 PM #9
I may be nit picking, but I'd be more concrned about the location of the return that close to the access hatch. How was it sealed? Did it have much insulation?
- Paul Fix
05-21-2007, 02:27 PM #10
Returns have almost no effect on room air patterns so I would say it is fine.
05-21-2007, 04:46 PM #11
Some HVAC systems have a return air sensor located in the return air duct. This is used to control a chilled or hot water valve. This type of sysetm works fine so a room stat located near a a ruturn should work as well.
06-01-2007, 09:45 AM #12
Perfectly OK in or around the return air location. This location will give a general indication of "mixed air temperature" within the home if air is properly returned from other spaces. (Undercuts, transfer grilles etc.)
06-01-2007, 02:04 PM #13
So, should the location of the return right next to the attic hatch be of concern?
- Paul Fix