04-15-2010, 07:50 PM #1
WATER HEATER AND BOILER VENT PIPES
HEY ALL
found this in crawl space today. two water heaters vented together but this opening in vent stack. same thing for boiler. am i right that this is spewing co into crawl. my co detector did read low levels when water heater fired. or is this a right config???
cvf
04-16-2010, 03:31 AM #2
Re: WATER HEATER AND BOILER VENT PIPES
unlisted horizontal draft hood. That and the single walled connector should not be there.
Listed and approved draft hoods only and B-vent only in crawl space.
Condition of chimney?
clean out?
Liner?
Clearances to combustibles off that single walled pipe?
Support?
Screws?
04-16-2010, 05:00 AM #3
If this is on the water vent pipe, it will act as a second draft hood, and double draft hoods are not permitted. It dilutes exhaust gases and might cause spillage into the crawlspace.
04-19-2010, 06:19 PM #4