    Jeff Eastman's Avatar
    Jeff Eastman Guest
    Default Restricted, crimped air ducts?
    May 2007
    Frankfort, KY
    Default Re: Restricted, crimped air ducts?
    Jeff,
    It wouldn't be a bad idea to recommend that they have the static pressure of the duct system tested to verify proper airflow.
    Any equipment attached to a duct system like that is in for a rough run.
    May 2007
    Frankfort, KY
    If you need a contractor in Vegas that does performance testing I can hook you up Jeff.
    One of the guys who mentored me lives in Vegas.
    Joseph Rago's Avatar
    Joseph Rago Guest
    Wink Re: Restricted, crimped air ducts?
    As a rule, flexible ductwork should not be installed in lengths greater than 8 feet, and with a bend greater than 90 degrees. One could test for "static pressure", but where? Suggest testing for volume delivered at each outlet for a more definitive result.
    Joseph D. Rago P.E.
    A.E.G.
    Yardley PA
    May 2007
    Frankfort, KY
    You could test the total external static pressure to see how much resistance the fan is seeing & you could also measure the static pressure drop of each suspect flex run out.
    Most guys can afford a manometer or magnehelic, most don't have anyway of measuring air volume from the registers.
    Quote Originally Posted by Joseph Rago View Post
    Where is that information from?
    Would like to read it.
    I know that flexible "air connectors" are not allowed longer than 14 feet, but "flexible duct" length is unlimited.
    Thanks.
    Why not install saddles below the ducts where the strap is restricting the air flow?
