Results 1 to 18 of 18
06-02-2009, 06:05 AM #1
Plumbing and electrical lines penetrating return air
Does the IRC specifically address plumbing and electrical penetrations into stud wall cavity or joist space plenum returns.
06-02-2009, 07:42 AM #2
Re: Plumbing and electrical lines penetrating return air
Talk about "Dumb and Dumber", and "Poor Planning" ... er ... "NO Planning".
From the 2006 IRC.
- Regarding the electrical:
- - E3804.7 Air handling—stud cavity and joist spaces. Where wiring methods having a nonmetallic covering pass through stud cavities and joist spaces used for air handling, such wiring shall pass through such spaces perpendicular to the long dimension of the spaces.
Those penetrations are also not sealed and are drawing in undesirable air (possibly contaminated air) into the return air system.
06-02-2009, 08:59 AM #3
I know according to the NEC u csny run electrical wires in the ductwork unless its in conduit.
06-02-2009, 09:45 AM #4
I know you are not allowed to have plumbing and other items in the return air plenum, such as gas lines, etc., but am having a mental fart in being able to find the code on it in the IRC. That is why I only posted the electrical code in the IRC.
Now, there are reference outside the IRC, but they would not be applicable as they would not specifically apply to a building which is under the IRC.
Think about the common sense aspect (lack thereof) of having plumbing pipe (and potentially sewer gas) in the return air duct.
06-02-2009, 11:54 AM #5
Jerry, you may be thinking of M1601.4 Under floor plenums although I'm not sure this would apply here since this appears to be limited to supply plenums and I did not take the time to really understand the situation in the OP.
06-02-2009, 12:10 PM #6
Jim,
That was the one in the IRC as the same requirements would need to be applied to return air plenums even though not specifically stated as such.
In the IMC the plenum section covers all plenums the same, which makes sense, and would make sense to apply that IRC supply plenum section to returns air plenums.
06-02-2009, 01:00 PM #7
So I was looking at the IRC regarding supply, but I am still unclear if that applies the returns. Regarding plumbing penetrations.
06-02-2009, 01:06 PM #8
06-02-2009, 01:11 PM #9
But the IMC doesn't apply to residential and the builder is in my face for the inspection. I told him the same you said it's common sense. But in the report I mentioned code and now everyone wants to know my reference. So the IRC doesn't prohibit it?
06-02-2009, 01:15 PM #10
That is where you take control and explain it to your client, do THEY want sewer gas (potentially) and other things in their home?
Have THEM call the city building department and talk to the inspectors. You do that also.
THEY are the ones who ultimately make the decisions.
The code is minimum and does not cover all things, not even all common sense things.
06-02-2009, 01:21 PM #11
That was my first move. I am impressed with my question, I stumped you for a min One more thing. The electrical and pass through the return as long as it's perpendicular to the vent.
06-02-2009, 03:17 PM #12
Yep, you did.
I think it is a bad idea, but, the code says it is okay if yada, yada, yada.
Of course, though, it needs to be sealed, and, do you really know it is "passing *through* perpendicular to the long dimension"?
Or does it enter there, run the long dimension a few inches or even a few feet, before passing through - that would not be allowed.
Of course, it has to be sealed ... oh, wait, I already said that didn't I?
Looks like PEX water line going in through the bottom with the DWV piping.
06-02-2009, 05:42 PM #13
Have to go back and look but I remember the code allows this if wood, does not if metal. Probably doesn't help without the reference number, but it's there.
06-03-2009, 06:06 AM #14
Since I am not a C-O-D-E inspector, I do not mention the word.
I will how ever reference construction standards, and make recommendations, and in this case I would have recommended that all penetrations be sealed in a approved manner, then I would have recommended that this condition be inspected by a licensed HVAC contractor as well as a Licensed Electrical contractor.
Good Luck
Tim
06-03-2009, 07:08 AM #15
I cite Code plenty but in these situations I don't even bother. Does not matter what the Code says. It's dumb, bad practice, unsafe however you want to put it. If explained properly to the client, they won't care what the Code is either. They won't want to live with it.
Air contamination, air infiltration, additional service work cost.
It looks like they are using two joist cavities side by side for return chases. Do both of those open up to one big floor grille in say the living or dining room. You can nail the builder on poor return air placement. Poor return air = higher energy costs.
06-03-2009, 07:32 AM #16
06-03-2009, 07:39 AM #17
The entire HVAC install was fubar. Jerry if you need to know that acronym email me.
06-03-2009, 07:44 AM #18