    Apr 2008
    McKinney Texas
    Default TXV Expansion valve insulation
    I usually write up TXV's that are not insulated. How many of you do the same ?
    Gene
    Default Re: TXV Expansion valve insulation
    Well Gene if there is condensation, it should be insulated. Typically this will just be the outlet of the valve and of course the suction line where the bulb is attached.
    Apr 2008
    McKinney Texas
    Jim thanks, I guess I thought the bulb should be insulated, thinking that would make the TXV more efficient. Maybe I am wrong.
    The bulb is just a temperature sensor clamped to the tail of the evaporator coil. The portion of the suction line exposed outside the cabinet (not the usual method) should be insulated to prevent condensation. If you are not getting a good thermal bond, the valve could malfunction and over or under feed the coil which would effect the operation and overall unit efficiency. Insulation would be a good thing at the bulb in that respect.
    Aug 2008
    Pleasant Hill, Iowa
    Hey Gene Jim is correct, the expansion valve bulb needs to be insulated because it is operating the valve to maintain the superheat of the evaporator. Normally the TXV valve itself is not insulated, but the suction line after the valve needs to be. Some TXV valves are automatic and some are adjustable to adjust the superheat. If the valve is inside the cabinet then don't worry about it, although some are on the outside of the cabinet or A-Coil.
    Dan Hagman ACI
    ProSite Home Inspections
    Des Moines, Iowa