    Jon mackay's Avatar
    Jon mackay Guest
    Default Condensing Furnace Air Intake Pitch
    I was not able to locate any tech info on this.
    Does the pitch of the air intake PVC from the exterior to the furnace matter? I was thinking no but a client asked the question and I couldn't say for sure.
    Jul 2007
    Chicago
    Default Re: Condensing Furnace Air Intake Pitch
    Pitch does not matter at the air intake however it does need to be the typical 1/4" per foot at the exhaust .
    Air intake opening does however need to be parallel with the ground and 12 inches above snow line when terminating outside.
    "Insure the combustion air inlet pipe (for a 2
    pipe installation) has a 90 degree termination
    elbow as shown in Figures 21 and 22.
    Figure 21. Alternate Horizontal
    Vent Installation
    Note: A combustion air intake must be provided
    with an elbow opening downward. The screen
    provided with the furnace must be installed in the
    elbow to prevent entry of debris or creatures."
    Quote Originally Posted by Bob Elliott View Post
    Vent Installation
    Bob - Not questioning the content of the above quote. Just wondering who/what it is from.
    Jul 2007
    Chicago
    It is from a general venting guide put out by ......
    NORDYNE condensing furnaces.
    You will however find others to be Similar.
    Also from the PDF......
    Furnace installation using methods
    other than those described in the following
    sections must comply with the
    National Fuel Gas Code and all applicable
    local codes to provide suffi cient
    combustion air for the furnace.
    Jon mackay's Avatar
    Jon mackay Guest
    Thanks for the info.
    Would you be able to post the pdf?
    Jul 2007
    Chicago
    Quote Originally Posted by Jon mackay View Post
    Looks like it fits so here you go.
    Attached Files Attached Files
    Jon mackay's Avatar
    Jon mackay Guest
    Thank you Bob, very helpfull