Thread: Combustion Air?
08-06-2007, 05:17 AM #1
Combustion Air?
Chapter 17 IRC requires an inlet and an outlet duct (one near ceiling/one near floor) for purpose of providing combustion air. Yet, I continually see one duct only in in ceilings of garages and laundry rooms. Could all of these be incorrect? Any info will be appreciated.
08-06-2007, 06:32 AM #2
Re: Combustion Air?
Tom,
Do they meet this?
From the IRC.
G2407.6.2 (304.6.2) One-permanent-opening method.One permanent opening, commencing within 12 inches (305 mm) of the top of the enclosure, shall be provided. The appliance shall have clearances of at least 1 inch (25 mm) from the sides and back and 6 inches (152 mm) from the front of the appliance. The opening shall directly communicate with the outdoors or through a vertical or horizontal duct to the outdoors, or spaces that freely communicate with the outdoors (see Figure G2407.6.2) and shall have a minimum free area of 1 square inch per 3,000 Btu/h (734
mm2/kW) of the total input rating of all appliances located in the enclosure and not less than the sum of the areas of all vent connectors in the space.
08-06-2007, 08:16 AM #3
Re: Combustion Air?
Combustion Air Sources
08-06-2007, 02:20 PM #4
Re: Combustion Air?
Now for the next question; do they really work?
08-06-2007, 02:54 PM #5
08-06-2007, 03:08 PM #6
Re: Combustion Air?
Thanks Guys for the info. Don't know how I ever got along without you.
08-06-2007, 04:23 PM #7
Re: Combustion Air?
"Note that this table Michael cites uses the incorrect units of BTU instead of BTU/h. Using BTU instead of BTU/h seems to be getting more common."
Bob,
Head right on over to Ft. Collins, and bust their chops:
http://fcgov.com/nbs/pdf/basement.pdf