    Default Comments on shared furnace / water heater vent
    Not sure if this is OK. The furnace has an induced draft blower (not a cat IV). The vent extends up about 6 feet then is nearly horizontal (about 1/4 inch fer foot of rise) for about 10 feet where it tees into the water heater vent, then vertical out the roof. Vent sizes all looked OK. All type B and clearances looked OK. What I'm not sure about is the induced draft shared with the standard water heater and the long nearly-horizontal run.
    Default Re: Comments on shared furnace / water heater vent
    What is your overall rise? Is there any evidence of condensation or improper function?
    I'd be calling for service prior to close of title. There is rust evident at the top and bottom of the access plate to the heat exchanger. Something amiss.
    Oct 2010
    Southwest US
    I would say the overall rise is about 20 feet. What I thought were condensation stains on the blower are actually stains from the humidifier above leaking. So no, no signs of improper drafting.
    Oct 2010
    Southwest US
    From the leaking humidifier I believe, but servicing is a good idea to see if there is permanent damage.
    James Duffin's Avatar
    James Duffin Guest
    How old is the installation? What you could be seeing is normal wear...
    Mar 2011
    Sparks,NV
    Nevada IOS#1730
    Nevada Energy Auditor #30