11-30-2011, 02:26 PM #1
Comments on shared furnace / water heater vent
Not sure if this is OK. The furnace has an induced draft blower (not a cat IV). The vent extends up about 6 feet then is nearly horizontal (about 1/4 inch fer foot of rise) for about 10 feet where it tees into the water heater vent, then vertical out the roof. Vent sizes all looked OK. All type B and clearances looked OK. What I'm not sure about is the induced draft shared with the standard water heater and the long nearly-horizontal run.
11-30-2011, 02:50 PM #2
Re: Comments on shared furnace / water heater vent
What is your overall rise? Is there any evidence of condensation or improper function?
11-30-2011, 03:04 PM #3
I'd be calling for service prior to close of title. There is rust evident at the top and bottom of the access plate to the heat exchanger. Something amiss.
11-30-2011, 03:06 PM #4
I would say the overall rise is about 20 feet. What I thought were condensation stains on the blower are actually stains from the humidifier above leaking. So no, no signs of improper drafting.
11-30-2011, 03:13 PM #5
11-30-2011, 04:12 PM #6
How old is the installation? What you could be seeing is normal wear...
11-30-2011, 10:42 PM #7
Here is some good info on venting. Common Venting of Gas Appliances | January 2011 Inspector eNews