Results 1 to 9 of 9
12-01-2011, 05:12 PM #1
Frost or ice on the outside of a heat pump compressor
Did an inspection where both heat pumps where loaded with frost on the outside of the units. The units were running at the time. Do heat Pumps go into a defrost mode when this happens. Eventually the ice melted. One of the systems did not preform adequately. Was this the result of that. It was not that cold, in the 40s.
Jim
12-01-2011, 05:25 PM #2
Re: Frost or ice on the outside of a heat pump compressor
Yes, heat pumps have a defrost cycle. The frost, or ice, on the coil will stop the airflow, so it has to defrost.
Read about Carriers heat pump defrost on page 4 of their manual.
12-01-2011, 05:40 PM #3
Thanks a lot Dom
Jim
12-02-2011, 06:05 AM #4
Low voltage wiring is incorrect.
Typically, someone other than the HVAC contractor familiar with the particular brand has worked on the units.
Did you notice if new programmable thermostadts were recently installed?
12-08-2011, 07:17 AM #5
The icing would be expected; todays "demand defrost" controls allow more ice to accumulate than previous control strategies. If it was that thick while you were there, then the fact that they both defrosted during your inspection is a good sign.
12-08-2011, 10:08 AM #6
12-08-2011, 01:41 PM #7
While we're on the subject... I've always wondered what causes the built-up on a straight A/C unit? I see it fairly infrequently (usually on the vapor line near the compressor) and write it up but don't know the cause. If I were to guess I'd think something in the system is clogged or not allowing the right flow of freon, etc.
12-08-2011, 02:40 PM #8
That is a low evaporator loading problem- not a refrigerant charge problem as is often presumed. Look for air flow restrictions and the like. Trust me, there is PLENTY of refrigerant in the system, just not enough heat (warm air) to evaporate it before it gets back to the compressor
12-08-2011, 08:02 PM #9