Had one today that had a 2004 Amana 92000 btu high eff. furnace. It was in a 3 foot deep by 4 foot wide closet off of the utility room. Had solid doors and was just vented to that closet only. Is there a certain size closet that this would be ok in or is it always wrong with solid doors? Thanks!
Similar Threads:E.D.S
Home Inspections
Lic.#450.010534
03-05-2012, 02:05 PM #2
Re: Combustion Air
Was there combustion air brought in from outdoors,and what did the rating tag say?
03-05-2012, 02:21 PM #3
Re: Combustion Air
No air of any kind brought to the closet or furnace.
E.D.S
Home Inspections
Lic.#450.010534
03-05-2012, 02:27 PM #4
Re: Combustion Air
Assuming no other source of combustion air, 92,000 BTU requires 4,600 cu/ft of confined space.
For an 8' ceiling that's 575sq/ft floor space, or 25x23'
If there were louvered doors opening to a similarly sized confined space they would need to supply 92sq/in of net free opening, which would translate (for typical restriction factors) to 123 sq/in of metal louvers or 368sq/in of wood louvers.
For a 12' wide wood louver, that would be around 30" in height.
For comparison, a 4x4x8' closet supplies 128 cu/ft, which will support a 5,560BTU appliance.
Also, keep in mind that you have to count all the gas appliances in the space, for example a gas clothes dryers (each needs around 200 cu/ft for combustion in addition to make-up air) and water heaters.
I have a spread-sheet I set up to calculate these requierments, if you let me know the BTU's of all appliances, I can give you the total requirements.
03-05-2012, 02:39 PM #5
Re: Combustion Air
Thanks a lot.
E.D.S
Home Inspections
Lic.#450.010534