Results 1 to 13 of 13
Thread: HVAC ducts in garage
01-23-2013, 09:02 PM #1
Is it correct that ductwork in garages are required to be enclosed in firerated sheetrock? Any comments on this?? Below is a picture of ducts in the garage another inspector said should be called out.
01-23-2013, 09:21 PM #2
Re: HVAC ducts in garage
No, ductwork is not required to be enclosed in firerated drywall.
The ductwork should be either 26 gage metal or "other approved material", and most/many AHJ accept ductboard as "other approved material".
Your photo clearly shows that ...
By the way ... flexible duct does not cut it (unless one installs a fire damper in the wall which will close off the duct opening through the wall.
01-23-2013, 09:24 PM #3
www.inspectaz.com
01-23-2013, 09:26 PM #4
01-23-2013, 10:05 PM #5
Thank you gentlemen
01-24-2013, 02:21 AM #6
If you are in New Jersey, the ducts in the garage should be insulated (both the supply & the return). Also, there should not be any openings (registers) in the garage.
01-24-2013, 04:42 AM #7
Yup, make sure duct work is sealed at cleats and penetrations through drywall in garage are sealed.
01-24-2013, 01:38 PM #8
01-24-2013, 04:26 PM #9
No openings are allowed in the garage.
01-24-2013, 05:12 PM #10
No openings into the garage from a system which also serves the living space. One can, if they so desire, insulate the garage and install a system for the garage space only with no interconnection to any system serving the living space. This is just to complicate the answer, but sometimes this is done.
01-24-2013, 05:50 PM #11
01-24-2013, 07:02 PM #12
Based on the IRC:
- ducts are allowed in the garage, with limitations on the material used for the construction of the ducts - the specifically approved material is 26 gage sheet metal, other material which is "approved" (meaning acceptable to the building official of the AHJ); 1" minimum thick duct board is also specifically stated as allowed in the Florida Building Code.
- *IF* you were to totally enclose flexible duct in a framed shaft with 1/2" gypsum board enclosing the flexible duct from the air handler to the wall, and everything was connected and sealed up tight ... then I suspect that the AHJ would allow flexible duct ... because it would not really be "in the garage" would it?
- all penetrations through the SEPARATION WALL (drop the term "firewall" as that wall is NOT a "firewall" - in most locations, a "firewall" may actually be required in some areas, but a "firewall" is not required by the IRC) - all penetrations into and through the separation wall need to be caulked and sealed around
Are you 'unconfused'?
01-24-2013, 07:15 PM #13
In simple terms..... Any HVAC system that is supplying conditioned air to a garage must be independent of any system that is supplying conditioned air to the interior living space of a home.