Results 1 to 12 of 12
05-08-2014, 11:22 PM #1
05-09-2014, 04:02 AM #2
Re: Determine electic furnace capacity
05-09-2014, 04:13 AM #3
Most of the time you can not tell by the tag. Some older units have the kw rating on them, others may have a clue in the model number, but many units do not come from the factory with heat strips installed, they are added after the fact.
On a recent inspection I found a Rheem heat pump. The m/n was RBHA21 J15SFAAI and it had 14.4 kw heat strips. You might conclude that the 15 was the heat strip rating.
I always open the front to get a look at the heat strips. Not only can you tell what size the unit is, but you also might find melted wires, etc. Once in a while, I find a heat pump without any heat strips installed.
05-09-2014, 04:42 AM #4
10 gauge AWG - 30 amp = 5 KW furnace
6 gauge AWG - 70 amp = 10 KW furnace
4 gauge AWG - 100 amp = 15 KW furnace
1 KW = 3,412 BTU per hour for heating
05-09-2014, 12:29 PM #5
05-12-2014, 05:27 AM #6
05-12-2014, 06:16 AM #7
Interesting. I see an electric forced air furnace maybe once every other year and a heat pump maybe once a year.
So, I would "assume" that a 15w unit would be for a relatively small home, 1100-1400 sq ft. in a cold climate.
05-12-2014, 05:54 PM #8
Hey Lonny, it's KiloWatts, not Watts.
We expect to see a 70 to 100 amp unit for an average smallish 3 bedroom house, and they go up to 125 amp. I don't recall seeing one bigger than 125 amp here but we have mild winters so the heat pump does the bulk of the heating.
50 amp is about the right size for a manufactured home.
Please remember to turn off the breaker before removing the cover. This is lethal voltages and the ends of the elements are exposed when you pull the cover, a big piece of metal.
05-12-2014, 06:03 PM #9
05-12-2014, 06:07 PM #10
05-12-2014, 06:24 PM #11
Fidel, just for you, two pics of an electric furnace. They are boring to see.
This one was interesting because the builder never got around to installing any ducts in the crawlspace. So I got a shot up into the furnace from below. It was toasty warm down there too.
05-12-2014, 06:39 PM #12