Results 1 to 28 of 28
06-25-2014, 11:45 PM #1
06-26-2014, 05:10 AM #2
Re: High efficiency furnace intake in garage
I assume you are asking about the combustion air intake and not the return air intake.
The combustion air has nothing in common with the conditioned air in an HVAC system, it is a non issue. Look up the brand you are posting about on the company website and you should be able to find an instalation guideline that shows how the Cat IV intake should be installed.
06-26-2014, 04:42 PM #3
Mr. Wood,
I'm shocked you are shocked at Scott's response. Was there some part that you don't agree with? I assumed that Darren was talking about combustion air, and not return air too.
06-26-2014, 05:02 PM #4
06-27-2014, 06:24 AM #5
06-27-2014, 01:46 PM #6
06-29-2014, 07:53 AM #7
06-29-2014, 10:21 AM #8
06-29-2014, 10:35 AM #9
When you draw combustion air from within the house (thermal envelope), you are using air that has been heated. Since the air was heated, this is a waste of energy. Also, The air that goes up/ out the flue has to be replaced. It is replaced with outside (unheated ) air, through cracks, around doors and windows.
06-29-2014, 10:41 AM #10
06-29-2014, 11:31 AM #11
Maybe its because I'm in backwards Tennessee, but we don't usually condition air in garages.
06-29-2014, 12:30 PM #12
I thought everyone had air conditioners in the garage, I do. Really.
(At one time I tried woodcraft. I had a window unit mounted. I had a really nice sawdust making machine. I could make the prettiest pile of sawdust you ever did see. I did make a cutting board once, but not much else. )
Getting back on topic
I am guilty of thread drift
OP said garage, then as I read on the conversation went to inside the house.
So I was speaking of drawing combustion air from inside the house.
I would still prefer not to draw air from the garage. I spent a lot of money to get that smell of fresh cut wood in the garage. Don't want it to get sucked out.
06-29-2014, 12:47 PM #13
And when that is done (it is allowed) the garage system is not permitted to be connected to the living area system, so what little is being wasted would be less than one opening of that big, huge, large garage door ... by the time the operator opens the door, and then closes the door, even for a person to walk through, the wasted energy going up the vent is like a mole hill next to Mount Everest - it is dwarfed in size.
06-29-2014, 03:48 PM #14
06-29-2014, 05:43 PM #15
That's great Kevin would you show us in this link taken from your web site that states you do this?
International Standards of Practice for Performing a General Home Inspection - InterNACHI
06-29-2014, 06:25 PM #16
06-29-2014, 07:40 PM #17
06-30-2014, 05:44 AM #18
And why would you need a picture?
The answer is correct. The installation manuals that come with high-efficiency units detail the requirements for sizing, methods of installation, locations, and spacing of intake and exhaust. These manuals are usually online at their respective websites. However for your enlightenment, in some cases intake may be in the garage and exhaust may be outside.
Again, I am amazed at your comment.
06-30-2014, 05:54 AM #19
Just a sidebar on this. When some contractors bid on a retrofit to a high-efficency system, some low ball by not extending the intake and exhaust to the outside, only the exhaust. But they may overlook make-up air as it may not be sufficient for the installation. An item to be looked at when inspecting.
06-30-2014, 05:57 AM #20
06-30-2014, 06:09 AM #21
Can someone show me any installation manual or code that drawing combustion air from a garage is allowed?
06-30-2014, 07:01 AM #22
06-30-2014, 07:53 AM #23
Is there a code issue with punching a hole for the intake (from the garage to conditioned space) through what may be a firewall?
06-30-2014, 02:59 PM #24
06-30-2014, 04:57 PM #25
06-30-2014, 06:16 PM #26
I know you asked for a manual and I don't have one handy but I am going to respond anyway. The logic I would use is that if you can have a water heater in the garage why couldn't you have a furnace? As long as the combustion chamber is sealed from the supply air stream (you'd better hope that it is) then I can't see why there would be an exclusion.
- - - Updated - - -
06-30-2014, 06:25 PM #27
06-30-2014, 07:52 PM #28
It's in the code .. "ignition source" is to be 18" above the garage floor.
"IGNITION SOURCE. A flame spark or hot surface capable of igniting flammable vapors or fumes. Such sources include appliance burners, burner ignitors and electrical switching devices. "
G2408.2 (305.3) Elevation of ignition source.
Equipment and appliances having an ignition source shall be elevated such that the source of ignition is not less than 18 inches (457 mm) above the floor in hazardous locations and public garages, private garages, repair garages, motor fuel-dispensing facilities and parking garages. For the purpose of this section, rooms or spaces that are not part of the living space of a dwelling unit and that communicate directly with a private garage through openings shall be considered to be part of the private garage.
- Exception: Elevation of the ignition source is not required for appliances that are listed as flammable vapor ignition resistant.
(while I am at it)
- G2408.2.1 (305.3.1) Installation in residential garages.
In residential garages where appliances are installed in a separate, enclosed space having access only from outside of the garage, such appliances shall be permitted to be installed at floor level, provided that the required combustion air is taken from the exterior of the garage.