Results 1 to 13 of 13
Thread: register in garage
08-28-2014, 10:09 PM #1
08-28-2014, 10:23 PM #2
Re: register in garage
No, not into garage if origin is home
08-29-2014, 08:33 AM #3
So this is not okay?
08-29-2014, 09:38 AM #4
08-29-2014, 09:54 AM #5
That does not look like combustion air.
It looks like a return, and no its not allowed.
08-29-2014, 10:37 AM #6
Don't forget the sediment trap also.
08-29-2014, 09:34 PM #7
Is it just me? Isn't that a downdraft furnace in the garage? Doesn't appear to be ductwork shared with the house. Looks like the furnace sits above the register. Cover for the furnace is in the lower right corner of the picture. Looks fine to me.
08-29-2014, 10:54 PM #8
It looks like a downdraft furnace with a register open to the garage but an establishing shot would be helpful.
Any conditioned air duct is not allowed to be open to the garage.
08-30-2014, 05:50 AM #9
08-30-2014, 10:45 AM #10
Is that duct board around the unit just there for looks (ugly looks, but still for looks) or is that the supply (or return) plenum?
If that is supply or return plenum, then the entire thing leaking air to the garage or sucking air from the garage.
08-30-2014, 01:20 PM #11
GARAGE DUCT INSTAllATION
R302.5.2 Duct penetration. Ducts in the garage and ducts penetrating the walls or ceilings separating the dwelling from the garage
shall be constructed of a minimum No. 26 gage (0.48 mm) sheet steel or other approved material and shall have no openings into the garage.
10-02-2014, 11:09 AM #12
No only if it has all solid 26 gage sheet metal all the way back to the unit to maintain the fire envelope
- - - Updated - - -
- - - Updated - - -
- - - Updated - - -
- - - Updated - - -
- - - Updated - - -
- - - Updated - - -
no only if 26 gage metal ducting to maintain fire envelope
10-02-2014, 11:42 AM #13