    Dave Rose's Avatar
    Dave Rose Guest
    Default Flex appliance connector?
    Would you categorize this as an FAC? If so, I thought the rules said you cannot run the FAC into any appliance "cabinet", which it does here.
    Do you see any other issues with this?
    Default Re: Flex appliance connector?
    Can't do it.
    G2422.1.2.3 (411.1.3.3) Prohibited locations
    and penetrations. Connectors
    shall not be concealed within, or
    extended through, walls, floors, partitions, ceilings or
    appliance housings
    It's wrong and I see it often..
    Dave Rose's Avatar
    Dave Rose Guest
    Thank you. Does anyone know the logic of why? It helps me to understand better. Is it concerns about damage where the flex enters perhaps from vibration etc.?
    Quote Originally Posted by Dave Rose View Post
    Dave,
    Yes. Furnaces, in particular, will vibrate during blower operation. This could result in the thin metal connector being abraded/cut through where it is fed through the furnace cabinet.
    I believe there is an allowance for flexible connectors through fireplaces though. I seem to recall a grommet needs to be there to provide protection. I cannot specifically recall the code section. Probably near 2422.1.2.3
    Dave Rose's Avatar
    Dave Rose Guest
    Dave,
    thank you, that helps.
    Oct 2010
    MONTREAL QUEBEC-CANADA
    411.1.3.3 and IRC G 2422.1.2.3
    Exception # 4 allows the listed appliance connector to enter the appliance to connect to the gas valve when protected by rubber grommet, plastic sleeve etc. to protect it from vibration from the motor.
    Aug 2008
    Pleasant Hill, Iowa
    The flex connector is used on Lennox Pulse furnaces because of the vibration, hard piping to a Pulse is not allowed. There are to be vibration eliminators in the gas line the supply and return duct, and the intake and exhaust have mufflers to control the noise. The flex connector is allowed around here by local jurisdiction because the door comes off easy and there is a rubber grommet used. This is not an issue around here and the connection will not come loose, a gas dryer vibrates more than a furnace and a flex is used there all the time.
    Dan Hagman ACI
    ProSite Home Inspections
    Des Moines, Iowa