Results 1 to 11 of 11
    Cape Cod, Massachusetts
    Default Vent Pipe contacting Gas Pipe
    Attached is an inspection I recently did.
    The single walled heating vent pipe was in contact with the gas pipe.
    I wrote it up as a a problem, but I couldn't find any reference in the code books. Anybody have any info on this?
    Aaron Miller's Avatar
    Aaron Miller Guest
    Default Re: Vent Pipe contacting Gas Pipe
    There's no problem with the gas pipe\vent connection. But . . .
    The flexible gas appliance connector is not properly protected where it enters the side of the furnace. And . . .
    There appears to be no gas shut-off valve for the furnace.
    Aaron
    Aaron,
    The shut off was above, but not shown in the picture.
    Thanks for the feedback.
    Ft. Myers, FL
    Am I wrong... that yellow gas flex line cannot enter the furnace cabinet????
    Paul Kondzich
    Ft. Myers, FL.
    It looks like that flex enters the cabinet quite well.
    You are correct in that it should not.
    What i'm seeing is instead of hard pipe being installed, people are just wrapping the flex with a section of foam insulation or electrical tape thinking that is going to be acceptable. What realtor started that as being ok?
    Also, I don't see any support strap for that vent where it goes horizontal and than there is the elbow.
    I'm more concerned about the slope (or lack of on the first section of Flue Pipe!).
    More than the lack of the first one foot not being a vertical rise?
    (Looked like it was sloped to me, but, from that angle, and no support, maybe it 'was' vertical when I saw it and now it a dropped? )
    Needs a NEW Flue System for sure, I'd take a CLOSE LOOK at all the Gas Appliances.
    After all Dead Clients ( or ones that are hospitalized Can't( won't REFER YOU,)
    Cool Re: Vent Pipe contacting Gas Pipe
    Good to see ya'll picking up on these defects:
    -lack of minimum vent connector rise
    -lack of support at either offset
    -no sign of mechanical fasteners at each joint including attachment to furnace collar
    -flexible appliance connector unprotected penetration of appliance cabinet ( some mfrs. may allow this is reasonable protected from chafing, blunt trauma or electrical bonding to cabinet.
    -vent connector slope
    What does it vent into? Is there a manifold with WH?
    Bob
    PS- ASHI show in New Orleans was pretty good, though low turnout
    Bob,
    Some mechanical fasteners 'are' visible in that photo. The other joints are not visible or taped over and may (or may not) have mechanical fasteners in them.