Thread: Gas furnace
    allen elliott's Avatar
    allen elliott Guest
    Default Gas furnace
    Any Ideas on what caused the soot around the vent. The picture was taken from the bottom side of the flue. It is an upflow furnace located inside an interior closet. It is fueled by propane. Thanks for the input.
    Default Re: Gas furnace
    Sorry, can't tell much from your picture, got any more? Bigger?
    Soot is usually (if not always) caused by incomplete combustion.
    Was there plenty of combustion and makeup air?
    Did any other appliances or the return air of the furnace itself upset the apple cart with all the doors to the equipment closed?
    Is the flue open and sized correctly?
    allen elliott Guest
    I am leaning toward the vent. It did not meet the 2-3-10 rule. It was very short and next to a wall on the roof.
    Quote Originally Posted by allen elliott View Post
    "Vents" do not have to meet that rule.
    By the way, it is also not 2-3-10, it is 3-2-10 for chimneys.
    Steve Lowery's Avatar
    Steve Lowery Guest
    What does the 3 refer to?
    For chimneys:
    3 feet high minimum (on sloped roofs you measure the height on the high side of the slope).
    2 feet minimum height above any part of any structure within 10 feet.