    I was told by another inspector that it is required to have the a/c condensing unit secured to the base pad but I am unable to find that anywhere in my code check book. Is this a manufacture requirement maybe?

    Similar Threads:
    Member Benefits1

  2. #2
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,040

    Default Re: Condenser unit hold down

    It is in the code and the manufacturer's installation instructions.

    The type, size, number, etc., of anchors would depend on the wind loads used in your area.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  3. #3
    Scott Murdock's Avatar
    Scott Murdock Guest

    Default Re: Condenser unit hold down

    Quote Originally Posted by Jerry Peck View Post
    It is in the code and the manufacturer's installation instructions.

    The type, size, number, etc., of anchors would depend on the wind loads used in your area.