Old 05-28-2007, 01:22 PM
dan orourke dan orourke is offline
breaker size
Old 05-28-2007, 01:58 PM
John Arnold John Arnold is offline
Re: breaker size
If AC plate says max 45, then max 45 it is. If 50 was ok, they'd say max 50.
This has been discussed a number of times, not that I'm suggesting you shouldn't have posted it, just a reminder that the archive is a great resource.
Old 05-28-2007, 04:14 PM
James Duffin James Duffin is offline
Re: breaker size
The problem is that 45 amp breakers are rare except at a real live wholesale house. The breaker or fuse should be 45 amps in this application. Check out 240.6 in the NEC for a run down on standard sizes. Good info to be had...
Old 05-28-2007, 04:51 PM
Richard Rushing's Avatar
Re: breaker size
- SECTION M1307- - APPLIANCE INSTALLATION- - - M1307.1 General. Installation of appliances shall conform to the conditions of their listing and label and the manufacturer's installation instructions. The manufacturer's operating and installation instructions shall remain attached to the appliance.
IRC 2003,
--E3602.11 Branch circuits for air-conditioning and heat pump equipment. The ampacity of the conductors supplying multimotor and combination load equipment shall not be less than the minimum circuit ampacity marked on the equipment. The branch-circuit overcurrent device rating shall be the size and type marked on the appliance and shall be listed for the specific purpose.
G2408.1 (305.1) General. Equipment and appliances shall be installed as required by the terms of their approval, in accordance with the conditions of listing, the manufacturer’s instructions and this code. Manufacturers’ installation instructions shall be available on the job site at the time of inspection. Where a code provision is less restrictive than the conditions of the listing of the equipment or appliance or the manufacturer’s installation instructions, the conditions of the listing and the manufacturer’s installation instructions shall apply.
Just because someone can't/won't take their arse to the supply house doesen't make it right. Write'em-up everytime.
Rich
Richard Rushing, HCRI
Duncanville, Tx.
Old 05-28-2007, 06:42 PM
Eric Barker's Avatar
Eric Barker Eric Barker is offline
Re: breaker size
Funny how many people don't understand the word "maximum."
I was at an evening H.I. meeting a couple of years ago. The HVAC company doing the presentation said that they frequently drop in breakers larger than the data plate listing and saw no problem with doing so. Then someone asked what happens to the compressor's warranty. The tech's response was that it would probably be voided. No duh! Least he was smart enough to realize that.
Eric Barker
Barrington, IL
Home inspection
Similar Threads
ridge vent size wes owens Attic Areas: Home Inspection and Commercial Inspection 8 03-13-2008 08:30 AM
Breaker position John Stephenson Electrical Systems: Home Inspection and Commercial Inspection 1 05-15-2007 07:19 PM
Humming breaker Jon mackay Electrical Systems: Home Inspection and Commercial Inspection 18 05-09-2007 06:41 AM
Size of condenser James Bohac Heating, Ventilation, Air Conditioning (HVAC): Home Inspection and Commercial Inspection 3 05-07-2007 07:01 PM
Psychedelic FP breaker BARRY ADAIR Electrical Systems: Home Inspection and Commercial Inspection 3 04-27-2007 01:10 PM
vB.Sponsors
Ad Management by RedTyger